Hi all,

I know tails are meant to be less than 3 metres in length and if not then a switch fuse needs to be installed.

What's the situation when the tails from a flat go from a communal hallway then into the consumer unit? (Approx 5m)

Do you just put a switch fuse next to the meter? (The run goes through the loft space)
 
The 3m rule is a DNO requirement, and normally results in a KMF or S/F being fitted.

It does not negate any need for RCD or mechanical protection if needed.
 
Eon are fitting an isolator on Friday so could I get them to fit a switch fuse instead?
 
Is it only 3 metres if there is no mechanical protection?

The tails are contained in some sort of plastic tubing all the way to the consumer unit.
 
fuse protection is DNO requirement

Mechanical protection is the regs, if it passes thro walls and floors or burried then it needs mechanical protection or RCD
 
Mechanical protection is the regs, if it passes thro walls and floors or burried then it needs mechanical protection or RCD

Sorry HT but may I correct one part of that...... Any cable going through a wall or ceiling and not embedded in the wall or ceiling does not need rcd or mechanical protection.
 
Ok Paul I will concede that. I
Typed it in a rush and diddnt make myself clear.

I was thinking more of passing through concrete slab.
 
Is it only 3 metres if there is no mechanical protection?

The tails are contained in some sort of plastic tubing all the way to the consumer unit.

Distance is a DNO requirement and is generally 3 to 5 metres. Then you require a switch fuse...

Plastic tubing IS a mechanical protection. Tails still need to be insulated and sheathed, as far as i'm aware!! SWA would also conform to to being insulated and sheathed, as well as providing improved mechanical protection....
 
Bullet> tails > Meter > tails > (Isolator) > tails > KMF > (RCD) > local tails.