not true split concentric cable can be used within the consumers fixed wiring and mechanical protection is not always a requirement

I'm no expert on split-con, but I must admit I thought it would still need mechanical protection OR RCD. When you say this is not always a requirement, when would this be? Cheers, Daz.
 
I'm no expert on split-con, but I must admit I thought it would still need mechanical protection OR RCD. When you say this is not always a requirement, when would this be? Cheers, Daz.
Whilst working with a DNO company. on many occasions when altering the main service cable, I've seen many NICEIC companies / electricians using split concentric cables. At first i didn't think it was allowed on the consumers side of the meter. But it is allowed.
 
Yeah, but it's not mechanically protected like SWA, so RCD needed if used on consumer side surely?? Daz
 
Yeah, but it's not mechanically protected like SWA, so RCD needed if used on consumer side surely?? Daz


This is where a bit of common sense comes into play!! If you're talking about running this cable direct buried then yes, an RCD would be required. Running the cable indoors under floorboards and up to the CU (in this case) surface fixed, (maybe in a white PVC conduit for aesthetic purposes) and i wouldn't have a problem not providing RCD protection on a TN installation!!
 
I spoke with a DNO engineer who "acquired" some split concentric cable to supply his garage...I think his theory being its no different to the cable in the street....
Never quite figured out why its ok for the DNO to bury split concentric, yet install it the same way across a domestic garden after the meter and its verboten by BS7671...
 
This is where a bit of common sense comes into play!! If you're talking about running this cable direct buried then yes, an RCD would be required. Running the cable indoors under floorboards and up to the CU (in this case) surface fixed, (maybe in a white PVC conduit for aesthetic purposes) and i wouldn't have a problem not providing RCD protection on a TN installation!!

Same as for T&E then - that was kind of my original point. Daz
 
I spoke with a DNO engineer who "acquired" some split concentric cable to supply his garage...I think his theory being its no different to the cable in the street....
Never quite figured out why its ok for the DNO to bury split concentric, yet install it the same way across a domestic garden after the meter and its verboten by BS7671...


Why would DNO ever bury split con?

Boydy
 
Never seen it buried D, except in street lighting when it is in ducting.

Coming straight off the street a supply would be unfused (sort of, as good as).

Boydy
 
Never seen it buried D, except in street lighting when it is in ducting.

Coming straight off the street a supply would be unfused (sort of, as good as).

Boydy

I may be getting confused here because I thought it was common practice. Is it just dual-con rather than split-con that they use for this? Daz
 
Is the meter outside?

You don't NEED to use SWA, unless it is going to be concealed in a wall (or run outside?). Remember, if the tails pass through an internal wall, this doesn't need to be SWA either. It will need fusing down (if an 80amp fuse in main cutout then use a 60amp) as well.

Kingeri , do you have a reg number for this, it's something I've seen before and it's cropped up on a job today where I have been asked to look at an installation on a new build - which is fairly crap! Cheers
 