Heres some more options not yet given too you so you have a choice.

1 Surface mount the tails
2 Bury DI tails more than 50mm along the whole route
3 Move the DB
 
I've had to edit multiple posts in this thread. One more abrasive comment and there will be infractions with no further warnings.
 
Those of you that have suggested using splitcon may like to consider the fact that it's not considered as satisfying the requirements for mechanical protection, so you'd still need an upfront RCD unless you were both clever and lucky with your routes. My call would be 16mm SWA into metalclad KMF and metal-backed CU (Hager do one - metal case but standard plastic front).....easy peasy.
 
Nobody got the easy option did they? If you can,t get the armoured in then let someone else do it.Why oh why did such a simple job end with someone getting wound up and getting a ban?
 
The usual nonsense.

Q
A
my question wasn't silly but you answer was.
My answer wasn't silly it was your question.

repeat ad nauseum with a few swear words thrown in.
 
I have installed lots of straight and split concentric on riser renewal programmes etc , the straight is a PME supply cable which is quite flexible as the outer is stranded , the split is not as flexible , half of the outer is neutral and the other half the earth , the centre core the live is alluminium , the cable is manufactured purely as a supply cable , we did use it at one time between a meter in either a communal area from a ryefield panel or an external cabinet to an FSMI or redhead in flats
but this is still considered a DNO supply cable , the split concentric cable is not to be used within the customers fixed wiring , there is no mechanical protection to the neutral as there is on SWA also this is a DNO supply cable only.
 
I have installed lots of straight and split concentric on riser renewal programmes etc , the straight is a PME supply cable which is quite flexible as the outer is stranded , the split is not as flexible , half of the outer is neutral and the other half the earth , the centre core the live is alluminium , the cable is manufactured purely as a supply cable , we did use it at one time between a meter in either a communal area from a ryefield panel or an external cabinet to an FSMI or redhead in flats
but this is still considered a DNO supply cable , the split concentric cable is not to be used within the customers fixed wiring , there is no mechanical protection to the neutral as there is on SWA also this is a DNO supply cable only.

not true split concentric cable can be used within the consumers fixed wiring and mechanical protection is not always a requirement
 