I have installed lots of straight and split concentric on riser renewal programmes etc , the straight is a PME supply cable which is quite flexible as the outer is stranded , the split is not as flexible , half of the outer is neutral and the other half the earth , the centre core the live is alluminium , the cable is manufactured purely as a supply cable , we did use it at one time between a meter in either a communal area from a ryefield panel or an external cabinet to an FSMI or redhead in flats
but this is still considered a DNO supply cable , the split concentric cable is not to be used within the customers fixed wiring , there is no mechanical protection to the neutral as there is on SWA also this is a DNO supply cable only.