Hi I have been asked to help with a temporary supply to a takeaway shop that has no electric meter.
I am thinking of Hiring a 10KVa generator to provide the supply but have never dealt with a job like this before.
Would love some opinions and guidance right now, would be much appreciated.
Also would the works be notifiable?
Thank
Apart from the obvious what's happened to the existing supply?
There are lots of issues around the generator.
Suitable site to locate it, where it won't get stolen, where the noise won't annoy the neighbours or the exhaust fumes won't cause and issue with the neighbours or the occupants of the Take away.
Suitable / secure site to store fuel in a suitable container (double skin / bunded) large enough to run the generator without constantly having to refuel it.
If the property is rented/leased the Landlord would need to agree to it, which I doubt they will.
The takeaway's Insurer will need to know about it and will possibly want a premium increase.
how has this situation arisen? takeaway shops don't spring up overnight, and electricity meters don't just vanish!
There are a lot of considerations to installing a generator, even temporarily. @snowhead has covered some of the points.
You also need to calculate the size of the generator required, taking in to consideration the run time you will get from the size versus actual load and also considering the quality of the generator. I've never yet seen a generator I would trust for this kind of application in less than a 20KVA rating.
Is there a timescale for when the meter will be fitted and a supply made available? It may be cheaper for them to remain closed for a while than it is to hire, fuel and operate a generator. Especially if environmental health take a disliking to it!
Notification isn't normally required for the actual electrical side of it, but there's a lot of other considerations to be made.
This is super helpful- Thank you
I've only had an initial conversation over the phone and will be meeting him shortly so hopefully will have more information later.
I have spoken to a generator supplier who can supply the gen set / fuel / cable all insured. But I will definately mention the above points to him.
Thanks again. Will update shortly ??
[automerge]1598026556[/automerge]
Cheers mate. Much appreciated. I'm meeting the chap later so will update on the chat later.
Had a quote for a 40KVA @ approx £1000/we which the owner surprisingly seemed happy about?
It's unusual for the hire company to provide insurance for any hired in plant, but they may have built the price of the brand of insurance they sell into the price.
That is not the only insurance you need to be concerned about though, your customers insurance company still needs to be informed as this will affect their premesis insurance due to increased risks. Plus the landlord if their is one will be in the same situation, their insurance may be affected.
Without knowing what is included in that price it is hard to comment on it.
Which hire company is that?
Something else you need to consider is phase balancing, you need to keep the three phases reasonably well balanced. Being too far out of balance for too long can damage the generator.
You will also need to consider fault protection, fuses, MCB's etc won't be able to provide fault protection due to the low prospective fault currents that a generator delivers. Most, but not all, hire generators these days incorporate a variable earth leakage relay on their output for this reason, it's up to you to check this and set it suitably for the installation as they are usually set down to minimum as supplied.
You cannot establish the PFC using a Zs test, and a low Zs test result does not mean that disconnection times will be met. These tests are fine on a DNO supply as it will always be capable of delivering the fault current, but with a small generator like this the voltage will droop as the engine bogs down, and probably stalls of/when a fault occurs.
Then there is earthing to consider, the generator will/should have a N-E link fitted which you will need to solidly reference to earth and probably keep separate from the DNO earth that may still be connected currently, but this needs assessment by a competent person.
Thanks Dave - much appreciated
After visiting the site it was deemed impractical to put a generator on site due to being surrounded by residential dwellings.
Hi Simon its me again ? with another electrical query....
I've been called to a bit off an odd job
Supplier has not given a date of when the new meter is being fitted so he spoke to his neighbour about borrowing a supply which she has agreed to.
The plan now is to put the neighbours supply into a Henly and split to feed both shops.
Its just a single phase supply but their really isn't much demand in the take away. So I'm planning to limit the supply to 40 amps through a small DB before his main isolator to limit demand on the neighbours. Also told him to unplug all non essentials.
The neighbours is a newsagents and is also not pulling much power.
Is there any reason why I cant do this?
Borrowing a supply from a neighbour? This could turn into a bit of a legal minefield with regards to billing etc. I would suggest putting in a meter and they agree a price per KW.
Reply to Temporary Supply to takeaway - Emergency in the UK Electrical Forum area at ElectriciansForums.net
I've been asked by a client to 'mask off' the green LED charging indictor lamps within several emergency lights fitted within bedrooms on a...
I'd appreciate the wisdom of the find minds here regarding this job. Yes, I've drifted into Wales again.... An extension is being planned as...
So far I have never had to deal with a new supply but a possible site we are looking at will need some major changes and so I wondered if folks...
Before I pay an electrician to come check my work, I thought it worth a post here. I don't want to pay the cost of a small car for a whole-house...