plan to install a 70mm swa into a 3 phase board.
my idea is to install a schneider acti 9, 3 phase board, with standard incomer etc, and install a schneider extension box below it. incomer or mcbs will only take say 25mm, so planning on using the extension box to reduce the 70mm swa down to say 25mm or 35mm with inline shearbolt connectors with heat shrink over. Thought using these i wouldn't need a hydraulic crimper. Do these conductors need to be fastened back via din rail, or is my method acceptable? whats your thoughts?
 
No like one of these that bolts to the acti9 board.

SEA9NI2504 | SCHNEIDER Acti9 250A 4P Switch Disconnector | BPX - https://www.bpx.co.uk/store/product/sea9ni2504.aspx

Use it in place of the extension box If you haven’t got room for both the external incomer kit and extension/spreader box. 70mm isn’t that difficult to manipulate in to position.
 
No like one of these that bolts to the acti9 board.

SEA9NI2504 | SCHNEIDER Acti9 250A 4P Switch Disconnector | BPX - https://www.bpx.co.uk/store/product/sea9ni2504.aspx

Use it in place of the extension box If you haven’t got room for both the external incomer kit and extension/spreader box. 70mm isn’t that difficult to manipulate in to position.
yeah that looks a good method, but the swa will be on an outgoing circuit, and going into a breaker, not the incomer , sorry. large cable due to lengthy run
 
yeah that looks a good method, but the swa will be on an outgoing circuit, and going into a breaker, not the incomer , sorry. large cable due to lengthy run
In that case it sounds like a horrendous design when taking installation and selectivity into account. I wouldn’t be feeding a distribution circuit that’s over 150 meters away using a mcb as it’s OCPD. I would be looking at either a fused switch, a switch fuse or an MCCB with selectivity being a major factor/consideration in the design.
 

Reply to terminating 70mm swa into 3ph board, best way? in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Has anyone fitted an SPD to a schneider standalone AFDD DB. Isobar P B Standalone Active distribution board, Acti9, 24 AFDD ways This board only...
Replies
4
Views
805
Hi I'm installing two new sub-mains. I need to parallel some of the supply cables. It's the main incomer in 5 x 25mm, with 5 x outgoing 25mm...
Replies
11
Views
2K
As a retired electrician, I need to specify a new type B board for a village church. Principal load is heating. Ipfc phase to phase is 1.1kA...
Replies
10
Views
1K
Hello All, new to the forum. Would be grateful for advice on whether the following proposal is an acceptable solution or open to any suggestions...
Replies
9
Views
5K
Basic question to see if what I wish to do is correct: Client wants to build (or is building) and outside room (roughly 8m by 4m) to be used as a...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock