Discuss terminating 70mm swa into 3ph board, best way? in the Commercial Electrical Advice area at ElectriciansForums.net
plan to install a 70mm swa into a 3 phase board.
my idea is to install a schneider acti 9, 3 phase board, with standard incomer etc, and install a schneider extension box below it. incomer or mcbs will only take say 25mm, so planning on using the extension box to reduce the 70mm swa down to say 25mm or 35mm with inline shearbolt connectors with heat shrink over. Thought using these i wouldn't need a hydraulic crimper. Do these conductors need to be fastened back via din rail, or is my method acceptable? whats your thoughts?
No like one of these that bolts to the acti9 board.
SEA9NI2504 | SCHNEIDER Acti9 250A 4P Switch Disconnector | BPX - https://www.bpx.co.uk/store/product/sea9ni2504.aspx
Use it in place of the extension box If you haven’t got room for both the external incomer kit and extension/spreader box. 70mm isn’t that difficult to manipulate in to position.
yeah that looks a good method, but the swa will be on an outgoing circuit, and going into a breaker, not the incomer , sorry. large cable due to lengthy run
In that case it sounds like a horrendous design when taking installation and selectivity into account. I wouldn’t be feeding a distribution circuit that’s over 150 meters away using a mcb as it’s OCPD. I would be looking at either a fused switch, a switch fuse or an MCCB with selectivity being a major factor/consideration in the design.
Reply to terminating 70mm swa into 3ph board, best way? in the Commercial Electrical Advice area at ElectriciansForums.net
Has anyone fitted an SPD to a schneider standalone AFDD DB. Isobar P B Standalone Active distribution board, Acti9, 24 AFDD ways This board only...
Hi I'm installing two new sub-mains. I need to parallel some of the supply cables. It's the main incomer in 5 x 25mm, with 5 x outgoing 25mm...
As a retired electrician, I need to specify a new type B board for a village church. Principal load is heating. Ipfc phase to phase is 1.1kA...
Hello All, new to the forum. Would be grateful for advice on whether the following proposal is an acceptable solution or open to any suggestions...
5K
Basic question to see if what I wish to do is correct: Client wants to build (or is building) and outside room (roughly 8m by 4m) to be used as a...