It says in GN8 to test between the MET and the suspected extraneous conductive part.

Not a problem in a domestic installation but a known/proven connection to earth is more practical in a commercial/industrial scenario.
 

Attachments

So, I carried out this test yesterday on some cable basket I put up for some Cat6 data cables. I tested between a known earth from a socket outlet and the cable basket and I got a reading of 0.47 ohms. Nice low reading via parallel paths (earthed structural metal work). I then bonded the basket using some 6mm.

So am I right in thinking that this needed bonding due to the reading, and if the reading had been above 23,000 ohms then it wouldn't have needed bonding?
 
I don't think it needed bonding. Here's a view from someone else;

 
If any current was entering that exotic French link then the Disconjoncteur tetrapolair de branchement would trip, can't see how any current could enter the TT earthing system without tripping something, perhaps even the Parafonudre Disconjoncteur Quata would go first.
 
There are safety procedures that we all go through before we carry out any work on a system, why are you persevering with this premise?
 