I can't see how the neutral can't be earthed at the TX, otherwise the neutral point will be all over the place unreferenced!!
That would be quick and easy.
The voltage is referenced to it’s self. In testing we always used either – or L2 for our earth free systems, it’s not referenced to earth it just a convenient way for us to record readings. We had both AC and DC systems.
Earth faults are a major headache, you don’t know they are there until you’ve got two of them on opposite lines. Durham mentioned the way ship bourn systems worked a while ago, I think it was similar to what we used.
View attachment 15139
If you want earth leakage detection then it gets complicated, the system we used for the 660V AC system used DC injection through chokes. It was a pain in the backside, it would trip at 20mA on a 2.6MW system.
Not sure how that would work on a distribution system covering several consumers, with different loads on different phases... And as you say RCD's (which they use in abundance) wouldn't functioning to well.