Hi chaps and chapettes,
I have a buried 6mm SWA 32a radial circuit powering a single 32a commando/ceeform, i'm looking to add a 16a ceeform for convenience. Can I use a thermal-magnetic breaker to derate to 16a. There isn't space for a 2 way CU so would this be my best option?
Thanks.
 
Hi chaps and chapettes,
I have a buried 6mm SWA 32a radial circuit powering a single 32a commando/ceeform, i'm looking to add a 16a ceeform for convenience. Can I use a thermal-magnetic breaker to derate to 16/15a. There isn't space for a 2 way CU so would this be my best option?
Thanks.
 

Attachments

  • Thermal breaker to derate circuit? bimetallic breaker.PNG - EletriciansForums.net
    bimetallic breaker.PNG
    202.8 KB · Views: 9
Yes you could, but I would not use the sort you pictured - it needs to be capable of breaking the worst case PFC/PSSC.

If you can fit in a garage CU or similar with a 16A MCB it will do the job, though you won't have any selectivity with the upstream one on a hard fault (but that probably does not matter here).
[automerge]1591632495[/automerge]
I see you can't fit one - not at all?

Another option is an HRC fuse as often they can break well over a MCB's capabilites, but typically they have DIN-rail sized holders as well. You might get away with a 32mm x 6mm fuse in a panel holder.
 
Thanks, was mainly curious to whether those bimetallic breakers (with an IP rated boot) can be used as such (other than on appliances) and makes perfect sense to use an mcb in a suitable enclosure. In this case ill just expand the backboard on the stake post (this is all external) and mount an ip rated consumer unit.
Was just being cost conscious.
 
Thanks, was mainly curious to whether those bimetallic breakers (with an IP rated boot) can be used as such (other than on appliances) and makes perfect sense to use an mcb in a suitable enclosure. In this case ill just expand the backboard on the stake post (this is all external) and mount an ip rated consumer unit.
Was just being cost conscious.
Often when in an appliance they are backed up by the supply fuse which will limit the current, or the nature of the load/control arrangement has other current limiting properties.

You probably would be OK, as under a hard fault the upstream MCB probably will trip first so it never has to break more than a few times its rating. But for fixed wiring you should stick to the IET regs which requires any breaker to be capable of interrupting the worst case PFC/PSSC at that point in the installation.

If space is an issue you might be able to fit something like this:

With a suitable 38x10 HRC fuse it will easily cope with fault currents.
 

Reply to Thermal breaker to derate circuit? in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock