If clearance of 50mm from the surface cannot be achieved capping should be used along with being rcd protected
Let an Arms member correct you sir:-
"If clearance of 50mm from the surface cannot be achieved capping should be used" = Are you on drugs or reading from a different book that we all do?
Greater then 50mm depth of the full circuit of the cable dose not need to be RCD protected unless it is for out door use, mobile equipment or in a special location. Capping is only for the protection of the plasterer if he's trowel is 3/4 the width of the chase.
CAPPING IS NOT MECHANICAL PROTECTION. PLEASE LETS MAKE THAT CLEAR TO ALL THAT IS READING THIS.