I have been asked to manufacture a control panel for an automated batch
feed mixer. Pic control unit conects to weigh bridge with 8 dil relays for
auger control. My question is this, one of the motors (the first one I've looked at) has terminals marked 1,2,3 and N. 1 to 3 are the phases N has the other end of the three windings connected together. I presume this makes it connected in STAR.
Why is the terminal marked as N ? should the star point not be connected to
earth :confused: The motor does looks old

regards Pat
 
not sure about the N terminal, probably a universal terminal block that manufacturer uses in other types of motor,but the star point should definately not be connected to earth,this should always be on a free terminal(in this case N ),earth terminal is for earth conductor only.
 
I have been asked to manufacture a control panel for an automated batch
feed mixer. Pic control unit conects to weigh bridge with 8 dil relays for
auger control. My question is this, one of the motors (the first one I've looked at) has terminals marked 1,2,3 and N. 1 to 3 are the phases N has the other end of the three windings connected together. I presume this makes it connected in STAR.
Why is the terminal marked as N ? should the star point not be connected to
earth :confused: The motor does looks old

regards Pat

Are the terminals linked out? And if so in what way?

Generally in all the older motors iv came across its been with copper links.

If the secondary terminals are linked out together its Star, if the terminals are linked out between the primary and secondary terminals then its Delta.

Hope this helps
 

Reply to Three phase motor question. in the Canada area at ElectriciansForums.net

Similar Threads

I want to check the insulation of the 3-phase 400VAC asynchronous squirrel cage motor. Motor's stator windings are connected in delta. I've read...
Replies
10
Views
2K
Hi gentlemen, I have three phase motor has an issue. This motor is star connection. When I just disconnect the power cable coming from MCC...
Replies
2
Views
1K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
I posted a month ago regarding a single phase motor + panel I have been given to try and sort following water damage to the panel. The assembly...
Replies
0
Views
1K
Hello, I am hoping this is in the correct forum. To start, I acquired a film processing machine that runs on 3 phase. Now before getting the...
Replies
19
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock