As per #35, is there any reason why you didn't carry out the full spread of tests?
When you say it works in single phase did you link out the incomer?
Am I missing something here you need to test this properly as has been said insulation testing a TPN supply is a 10 point test
You obviously have a problem between l1 and l2 if you put power onto l1 and test l2 do you get a voltage
The fact that the fuses blow when l1and l2 are energised suggests that you are shorting 2 phased together
I would look at that poor termination of the armour it should be glanded properly even though your not relying on the armour.
Have you nicked the insulation of the cores as you have cut and terminated the armour
I would advise this isn't energised to try and find out.
its almost beyond words innit....lol...Its crying out for a voltage tester to be put on top side of L2 L3 carriers on the ryefield to see if L1 is coming back from the DB.
Still, impressed he is happy to bang the fuses in without doing the IR, i guess eventually when he has had a few systems blow up in his face he may value the simple process of getting the tester out and prodding the install for what? 49 seconds to make sure its safe to energise but hey ho.....
Hi, just did a three phase consumer unit