I refer you to the first line of post number 13.

I can post your long list of faults if you want! :sifone::biggrinjester:
 
As always instead of advice people just talking nonsense obviously I will check all wiring and test before replacing. incomer but as incomer was used and is rattling inside I will need to replace and carry out further tests.
Guess I am on my own no useful advice !
 
What exactly are you talking about, when you say it was ''Used'' and ''Rattling Inside''??

I think most people here, have been thinking you were talking about a cable when you stated ''Incomer'', but your not are you!!
 
What exactly are you talking about, when you say it was ''Used'' and ''Rattling Inside''??

I think most people here, have been thinking you were talking about a cable when you stated ''Incomer'', but your not are you!!
probably his own head he was shekkin....
 
So are we to assume this "incomer switch" is the isolator between the meter and the ryefield?
 
Asks for advice, struggles with terminology, fails to express the problem with any clarity, doesnt provide info when asked, spits dummy out, insults forum.
Its like I have deja vu.
 
Asks for advice, struggles with terminology, fails to express the problem with any clarity, doesnt provide info when asked, spits dummy out, insults forum.
Its like I have deja vu.

For your information I do not struggle with terminology and am educated thank you
 
Thanks to all who responded productively, the supply is 3 phase 420v fused by two 100a and one 60a this is fed Into ryefield board 5 way which is feeding shop and 2 flats by of 5 60a fuses. See pictures attached. This is then fed using armoured cable to db. Have done continuity tests live phases to earth and neutral no fault found. Insulation resistance is 675m ohm and passes fine. When I fit l1 fuse in ryefield db works fine, however if I fit l2 fuse and test it blows fuse l1 and l2 but the flats are unaffected as they are fed direct off supply. Any productive help will be appreciated. By the way phases are correct and even if they would not that should not blow fuse on ryefield.
 

Attachments

  • uploadfromtaptalk1375661697954.jpg
    uploadfromtaptalk1375661697954.jpg
    84.5 KB · Views: 141
  • uploadfromtaptalk1375661720737.jpg
    uploadfromtaptalk1375661720737.jpg
    69.6 KB · Views: 162
  • uploadfromtaptalk1375661737352.jpg
    uploadfromtaptalk1375661737352.jpg
    52.5 KB · Views: 138