Was testing a EV charge point today and noticed the internal RCD was TP device with only a single phase supply and load in use (L1).

There was 245V either side of the RCD but the test button didn't function.!!

Is it possible the test button is fed from one of the phases that is not used, (L2,L3).

The RCD tested OK at 1x & 5x.

This looks to be how the charger was manufactured.

Anyone seen similar?
 
I know if you want to use a 4 pole RCCBs without a neutral you would insert a resister (correct valve for rcd) between an outgoing phase and neutral terminal. (See Schneider link)

I assume your correct the test button must be linked through an output, sounds to me like a manufacturers fault.
 

Attachments

  • EUR125.30-3A.pdf
    284.7 KB · Views: 7
  • Connnection in 3P RCCB-2.pdf
    62.3 KB · Views: 6
The diagram on the rcd usually shows which phase the test button is on.

<satire>
Although it almost certainly failed recently as it must have worked on each of the 6 monthly tests routinely carried out
</satire>
There must be thousands of EV chargers that are serviced annually, as the ones I do are.

We do test the RCD but only annually.
 
There must be thousands of EV chargers that are serviced annually, as the ones I do are.

We do test the RCD but only annually.
I was only making comment about the number of rcd with the test 6 monthly label, yet hardly any are, in all honesty, I haven't checked mine within 6 months!

The test button is usually l2- n , but not always, but the diagram on the rcd shows which phase it's connected to
 

Reply to Three phase Type A RCD confusion. in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock