C

charlie

Why on a caravan site or some other outbuilding does the earth have to be an earth electrode and not the earthing on the supplying TN-C-S ???
 
Why on a caravan site or some other outbuilding does the earth have to be an earth electrode and not the earthing on the supplying TN-C-S ???
Your main earth on a TNCS system is actually connected to the neutral conductor. If the electricity boards supply neutral went down there would be no neutral or earth. Thus anything that should be neutral or earth will become live. Hence the stake.
Sounds good anyway!!!!. I'm sure thats right.
 
Your main earth on a TNCS system is actually connected to the neutral conductor. If the electricity boards supply neutral went down there would be no neutral or earth. Thus anything that should be neutral or earth will become live. Hence the stake.
Sounds good anyway!!!!. I'm sure thats right.

pretty much, Regman, although given that the neutral is live anyway....

way is see it, N is earthed at the substation tranny, Supply N goes open circuit, load is drawing current, current will try to continue flowing to PME connection point at dis board, through neutral to open circuit, then down through nearest PME spike and back to origin

but of course, current flow through resistive earth path, V=IR, so a PD will develop on the installation earth system, which will have a different PD to the local earth and extraneous conductive parts (step and touch voltages anybody;))

this is the danger with the TNCS, in that the N &E are the same point in the installation incoming supply, and the circuit current will try to use the earth path in the event of the N going o/c
 

Reply to TN-C-S + earthing in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Can a domestic consumer unit feed another consumer unit, via the Main Switch. Details are: domestic property with 100A single phase supply...
Replies
9
Views
438
Evening Chaps As can be seen in the attached photo , the incoming supply cable has a Earth soldered to the outer sheath of the cable suggesting...
Replies
10
Views
1K
I've tried to understand one way or another but this seems to be connected to the DNO fuse/cutout, and then loops down (out of sight) and comes...
Replies
2
Views
732
Now Ive done Periodic Inspection and Initial Virification Qualifications with LCL/EAL (so non C&G 2394/95) # strange part building Modules , this...
Replies
6
Views
944
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
721

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock