Hi knowledgeable collective.

To the chase. TN-S Megger 1553

2 wire Ze 0.09 but was getting Zs on cooker cable 1.5 metre long using No trip 3 wire got 33.4ohms So went back through system right to isolator post meter and was still getting 33 ohm reading. So 2 wire uses higher current so might overcome a flakey connection but to this extent? Chucked meter on home circuit as was doubting meter measured normal. Back tomorrow to try to reveal top of incomer then prob onto DNO but would like to know what might be occuring.
 
Did you try 2 wire Zs@DB or at isolator?
I'd be very surprised if this was anything to do with 2/3 wire test.
First question is are you sure you reconnected the earth properly after Ze?
It sounds like a loose live tail at isolator, meter or cut-out, or loose main earth conductor.
 
Did you try 2 wire Zs@DB or at isolator?
I'd be very surprised if this was anything to do with 2/3 wire test.
First question is are you sure you reconnected the earth properly after Ze?
It sounds like a loose live tail at isolator, meter or cut-out, or loose main earth conductor.
Hi, Thanks for your thoughts. 2 wire test at main isolator 0.07 I think. 3 wire 33.3. I think it must be a bad connection just wondering what & why such a big disparity.
 
Hi, Thanks for your thoughts. 2 wire test at main isolator 0.07 I think. 3 wire 33.3. I think it must be a bad connection just wondering what & why such a big disparity.
Oh sorry, didn't twig you were measuring 2 and 3 wire at same point. As you say they are a mile apart and that is indeed interesting.
As the 2 wire test uses Live and Earth, and the 3 wire obviously adds Neutral, I'm just wondering what effect a loose N conductor would have on the test result....
I wouldn't be happy until I knew why either.
 
Most likely is uplift caused by RCD or MCB. try a 3 wire no trip on the outgoing of the RCD.
 
Most likely is uplift caused by RCD or MCB. try a 3 wire no trip on the outgoing of the RCD.
We are reading it differently - think he’s saying at isolator at intake he’s getting wildly different reading for 2 wire and 3 wire tests.
Upstream of CU by sounds of it.
 
Have you done a two lead test between L&N?
 

Reply to TN-S High Ze measured 3 wire no trip. in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock