Hi knowledgeable collective.
To the chase. TN-S Megger 1553
2 wire Ze 0.09 but was getting Zs on cooker cable 1.5 metre long using No trip 3 wire got 33.4ohms So went back through system right to isolator post meter and was still getting 33 ohm reading. So 2 wire uses higher current so might overcome a flakey connection but to this extent? Chucked meter on home circuit as was doubting meter measured normal. Back tomorrow to try to reveal top of incomer then prob onto DNO but would like to know what might be occuring.
To the chase. TN-S Megger 1553
2 wire Ze 0.09 but was getting Zs on cooker cable 1.5 metre long using No trip 3 wire got 33.4ohms So went back through system right to isolator post meter and was still getting 33 ohm reading. So 2 wire uses higher current so might overcome a flakey connection but to this extent? Chucked meter on home circuit as was doubting meter measured normal. Back tomorrow to try to reveal top of incomer then prob onto DNO but would like to know what might be occuring.