Hi knowledgeable collective.

To the chase. TN-S Megger 1553

2 wire Ze 0.09 but was getting Zs on cooker cable 1.5 metre long using No trip 3 wire got 33.4ohms So went back through system right to isolator post meter and was still getting 33 ohm reading. So 2 wire uses higher current so might overcome a flakey connection but to this extent? Chucked meter on home circuit as was doubting meter measured normal. Back tomorrow to try to reveal top of incomer then prob onto DNO but would like to know what might be occuring.
 
Did you try 2 wire Zs@DB or at isolator?
I'd be very surprised if this was anything to do with 2/3 wire test.
First question is are you sure you reconnected the earth properly after Ze?
It sounds like a loose live tail at isolator, meter or cut-out, or loose main earth conductor.
 
  • Like
Reactions: Jim_e_Jib
Did you try 2 wire Zs@DB or at isolator?
I'd be very surprised if this was anything to do with 2/3 wire test.
First question is are you sure you reconnected the earth properly after Ze?
It sounds like a loose live tail at isolator, meter or cut-out, or loose main earth conductor.
Hi, Thanks for your thoughts. 2 wire test at main isolator 0.07 I think. 3 wire 33.3. I think it must be a bad connection just wondering what & why such a big disparity.
 
Hi, Thanks for your thoughts. 2 wire test at main isolator 0.07 I think. 3 wire 33.3. I think it must be a bad connection just wondering what & why such a big disparity.
Oh sorry, didn't twig you were measuring 2 and 3 wire at same point. As you say they are a mile apart and that is indeed interesting.
As the 2 wire test uses Live and Earth, and the 3 wire obviously adds Neutral, I'm just wondering what effect a loose N conductor would have on the test result....
I wouldn't be happy until I knew why either.
 
  • Like
Reactions: Jim_e_Jib
Most likely is uplift caused by RCD or MCB. try a 3 wire no trip on the outgoing of the RCD.
 
Most likely is uplift caused by RCD or MCB. try a 3 wire no trip on the outgoing of the RCD.
We are reading it differently - think he’s saying at isolator at intake he’s getting wildly different reading for 2 wire and 3 wire tests.
Upstream of CU by sounds of it.
 
Most likely is uplift caused by RCD or MCB. try a 3 wire no trip on the outgoing of the RCD.
That was my initial thought, but such a high figure. Then found I was getting pretty much the same reading everywhere. Seems to be related to the income as all else isolated off.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Frome
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
Business Name
BB Electrical

Thread Information

Title
TN-S High Ze measured 3 wire no trip.
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
8

Advert

Thread statistics

Created
Bruno Branson,
Last reply from
Bruno Branson,
Replies
8
Views
1,298

Advert