Hi all, just wanted to see what the collective thoughts are on readings obtained when testing end to ends on a ring mains cpc’s. If I were to use the 1.67 calculation for a 2.5/1.5 twin and Earth cable, what kind of reading would people allow to be recorded before considering coding it on the cert. Would you code it if the results obtained don’t match the 1.67 calculation exactly or would you allow a 10% tolerance?
Thanks
 
Hi all, just wanted to see what the collective thoughts are on readings obtained when testing end to ends on a ring mains cpc’s. If I were to use the 1.67 calculation for a 2.5/1.5 twin and Earth cable, what kind of reading would people allow to be recorded before considering coding it on the cert. Would you code it if the results obtained don’t match the 1.67 calculation exactly or would you allow a 10% tolerance?
Thanks
How much over the top is the reading? If it's an old property you may find that some of the cable is 2.5/1,0. Recalculate as 1.0 cpc to see if that comes close to your readings, if it does pull off some of the face plates and check.
 
Hi, let’s say it is 2.5 and 1.5 Earth, the calculated reading should be 0.50 but you’re getting 0.80, would you code it a c3? the live and neutrals have the 0.05 tolerance just wondered if people apply that to the Earth also
 