Snapester

Got called out to a burnt out fuse carrier on Wylex rewireable CU! Classic! It was a 1361 carrier with a 30amp fuse that hadn't blown but the board was melted pretty good!
R1+R2 the circuit to find out which one it was, located it to the shower circuit, which tested good 0.11 from board to shower, but the isolation switch was broken possibly burnt out i expect having never been turned off in its life duration.
No signs along the circuit of over heating although the cable was 4mm undersized for its use.

What could of coursed such an overload do you think, i could only put it down to bad connection in switch or shower not been correctly turned off after use? Ideas?

Cheers
 
In my experience the burning is usually confined locally to the weakest link, be it the cable itself, or a high resistance joint, I would expect it to be either at the fuse to board interface itself, or possibly to the terminations to the fuse carrier terminal.

See what others think.
 
Last edited:
as above. bad connection at the fuse.
 
Yeah well I usually would say most resistive joint but it was locked tight into the carrier! Strange but I guess it would have to be as the overheating was only there!
 
detail of damage 2.jpg

Yep weakest part of a heavy load circuit I have lost count of the burnt out shower switches I have had to replace plus a CU as above all due to slack connections
 
And that is why I hate rewireables. Should be outlawed across the country. Horrible things and lethal. If I was a millionare i would get a campaign agaist them going, only place they should be is in the bin!!
 
Just to add if you look at the picture that was the second time it happened plus me thinks the owner did a quick repair but with a blunt screwdriver mind should not complain its good business for me
 

Reply to Tonights Callout. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening Gents just after a bit of advice and what would you do differently. I have wired up 3 kw heaters in 4mm tuff cable (40 meter distance...
Replies
2
Views
242
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K
This from a while ago but reading about everyone elses problems tonight made me remember this one. The original job was the lights in a recent...
Replies
1
Views
989
I try to keep out of Domestic work but I have a problem at home. Currently I have a wylex fuse board with re-wire fuses. they are great because...
Replies
55
Views
4K
Hi all, Been browsing these forums for a while, always great to learn a new way to skin the same cat. Anyway, cut a long story short, was an...
Replies
11
Views
576

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock