Snapester
Got called out to a burnt out fuse carrier on Wylex rewireable CU! Classic! It was a 1361 carrier with a 30amp fuse that hadn't blown but the board was melted pretty good!
R1+R2 the circuit to find out which one it was, located it to the shower circuit, which tested good 0.11 from board to shower, but the isolation switch was broken possibly burnt out i expect having never been turned off in its life duration.
No signs along the circuit of over heating although the cable was 4mm undersized for its use.
What could of coursed such an overload do you think, i could only put it down to bad connection in switch or shower not been correctly turned off after use? Ideas?
Cheers
R1+R2 the circuit to find out which one it was, located it to the shower circuit, which tested good 0.11 from board to shower, but the isolation switch was broken possibly burnt out i expect having never been turned off in its life duration.
No signs along the circuit of over heating although the cable was 4mm undersized for its use.
What could of coursed such an overload do you think, i could only put it down to bad connection in switch or shower not been correctly turned off after use? Ideas?