@DPG He doesn’t even know what an amprobe is and don’t own oneDo not connect an ammeter directly across live/hot and neutral!!
@DPG He doesn’t even know what an amprobe is and don’t own oneDo not connect an ammeter directly across live/hot and neutral!!







Ofdteve according to the NEC the first disconnect after the transformer you can terminate the grounding conductors and the grounded conductors together. IF YOU SUB-FEED another panel then you have to isolate the grounding conductors and the grounded conductors. As far as the breakers go they have two jobs to do one is short circuit and the other is heat or over current Example if you have a 20 amp breaker and you are drawing just say 25 amps I don’t care how cold it is that wire can heat up enough To burn the house down if that breaker don’t do it’s jobInteresting, I always thought breakers worked by sensing some type of electromagnetic field, not by sensing heat. Doesn't that make the breakers inherently very inaccurate or inconsistent in protecting the circuits? When its hot, say 95*F, the breakers will be much warmer and more likely to flip than when its below freezing at, say 10*F?
Below is my house breaker breakdown in case the seven attached pictures aren't clear. Where two or four amp amounts are listed, that's just two or four breakers connected together. The numbers 1 through 16 correspond to the numbers and their breakers in the pictures.
I was mistaken when I said more than one wire was connected to some breakers, however, the common neutral and earth ground wires are all connected together. I don't understand how that is safer than having them as separate circuits.
1 - 20 amp
2 - 20 amp
3 - 30 & 30 amp
4 - 20 & 20 amp
5 - 20 & 20 amp
6 - 20 amp
7 - 20 amp
8 - 20 & 20 amp
9 - 15 amp
10 - 15 amp
11 - 30 & 30 & 30 & 30 amp
12 - 30 & 30 amp
13 - 50 & 50 amp
14 - 20 amp
15 - 20 amp
16 - 20 amp
So is the next step to purchase another sub-panel breaker box and wire it to the wires coming out of the meter?
Thank you, gentlemen, for your comments and help.
View attachment 52731View attachment 52732View attachment 52733View attachment 52734View attachment 52735View attachment 52736View attachment 52737
[automerge]1569803532[/automerge]
Quote: He doesn’t even know what an amprobe is and don’t own one
In my younger days I used to repair electronic equipment for a living and own a couple ohm meters that can measure amps in addition to voltage and resistance. However, I've only worked with milli and micro volts / amps, nothing lethal. But the principles are all the same, just the hardware to control the electricity is different.
Oddteve as far as the breaker rating goes you have quite a few 240vac loads, again what you have is legal and safe. Remember I told you that you have a calculated load and a connected load. It is legal and safeInteresting, I always thought breakers worked by sensing some type of electromagnetic field, not by sensing heat. Doesn't that make the breakers inherently very inaccurate or inconsistent in protecting the circuits? When its hot, say 95*F, the breakers will be much warmer and more likely to flip than when its below freezing at, say 10*F?
Below is my house breaker breakdown in case the seven attached pictures aren't clear. Where two or four amp amounts are listed, that's just two or four breakers connected together. The numbers 1 through 16 correspond to the numbers and their breakers in the pictures.
I was mistaken when I said more than one wire was connected to some breakers, however, the common neutral and earth ground wires are all connected together. I don't understand how that is safer than having them as separate circuits.
1 - 20 amp
2 - 20 amp
3 - 30 & 30 amp
4 - 20 & 20 amp
5 - 20 & 20 amp
6 - 20 amp
7 - 20 amp
8 - 20 & 20 amp
9 - 15 amp
10 - 15 amp
11 - 30 & 30 & 30 & 30 amp
12 - 30 & 30 amp
13 - 50 & 50 amp
14 - 20 amp
15 - 20 amp
16 - 20 amp
So is the next step to purchase another sub-panel breaker box and wire it to the wires coming out of the meter?
Thank you, gentlemen, for your comments and help.
View attachment 52731View attachment 52732View attachment 52733View attachment 52734View attachment 52735View attachment 52736View attachment 52737
[automerge]1569803532[/automerge]
Quote: He doesn’t even know what an amprobe is and don’t own one
In my younger days I used to repair electronic equipment for a living and own a couple ohm meters that can measure amps in addition to voltage and resistance. However, I've only worked with milli and micro volts / amps, nothing lethal. But the principles are all the same, just the hardware to control the electricity is different.
I’m sorry you barked at me but you are barking up the wrong tree. unlike you I know what I’m doing and got my master license to proof itInteresting, I always thought breakers worked by sensing some type of electromagnetic field, not by sensing heat. Doesn't that make the breakers inherently very inaccurate or inconsistent in protecting the circuits? When its hot, say 95*F, the breakers will be much warmer and more likely to flip than when its below freezing at, say 10*F?
Below is my house breaker breakdown in case the seven attached pictures aren't clear. Where two or four amp amounts are listed, that's just two or four breakers connected together. The numbers 1 through 16 correspond to the numbers and their breakers in the pictures.
I was mistaken when I said more than one wire was connected to some breakers, however, the common neutral and earth ground wires are all connected together. I don't understand how that is safer than having them as separate circuits.
1 - 20 amp
2 - 20 amp
3 - 30 & 30 amp
4 - 20 & 20 amp
5 - 20 & 20 amp
6 - 20 amp
7 - 20 amp
8 - 20 & 20 amp
9 - 15 amp
10 - 15 amp
11 - 30 & 30 & 30 & 30 amp
12 - 30 & 30 amp
13 - 50 & 50 amp
14 - 20 amp
15 - 20 amp
16 - 20 amp
So is the next step to purchase another sub-panel breaker box and wire it to the wires coming out of the meter?
Thank you, gentlemen, for your comments and help.
View attachment 52731View attachment 52732View attachment 52733View attachment 52734View attachment 52735View attachment 52736View attachment 52737
[automerge]1569803532[/automerge]
Quote: He doesn’t even know what an amprobe is and don’t own one
In my younger days I used to repair electronic equipment for a living and own a couple ohm meters that can measure amps in addition to voltage and resistance. However, I've only worked with milli and micro volts / amps, nothing lethal. But the principles are all the same, just the hardware to control the electricity is different.
Steve I’m sorry also that panel looked full and you don’t need another meter I just buy a 60 amp 16 circuit main lug only panel. Mount it where you want. Please take 1 of the 20 amp double pole breakers out and buy a 60 amp double pole breaker to feed your new panel, then you can also put that 20 amp breaker you took out in your new panel. Run # 6 wire x 3 and 1 # 10 ground wire to your new panel. I wish you the best of luck and don’t hesitate to contact me. If you have an extra space for the 60 amp breaker in your panel you don’t need to remove the 20 amp breaker. Best of luck and no hard feelings. That remark about no amprobe was made because I thought you said you was a DIY. no hard feelingsI don't doubt you know what you are doing, that's why I come to you for advice. And I apologize if you think I barked at you, that was not my intention. I just had to clarify when someone assumes and makes an untrue statement about me I'm compelled to correct the statement - I do own meters capable of reading low amps and I do know how to use it inline within a circuit. But I don't presently have anything capable of reading something like 50 amps. But if you tell me I need to purchase such a meter to complete this project, then I will do so as I've always considered you the expert in this field.
Moving along, my last question still stands:
So is my next step to purchase another outdoor master or sub-panel breaker box and wire it to the wires coming out of the meter?
Thank you, Sir, for your help.
Interesting, I always thought breakers worked by sensing some type of electromagnetic field, not by sensing heat. Doesn't that make the breakers inherently very inaccurate or inconsistent in protecting the circuits? When its hot, say 95*F, the breakers will be much warmer and more likely to flip than when its below freezing at, say 10*F?
Steve yes you can take out the 2 singles out and put you 60 in them slots. 75 miles is a lot plus rain and hail wow it’s 90 + degrees I NC and so humid are they a Lowe’s or Home Depot bear you. As far as the price the only thing I can think of is that make sure you get a 60 amp double pole breaker with the same name brandWow, so simple, I wonder why I didn't think of that. The nearest store that sells electrical hardware is 75 miles away in Klamath Falls, Oregon. I'll get a main lug only panel this weekend and hopefully install it next week after work providing the rain and hail lets up. I'll then post pictures here to get your feedback if I wired everything safely before I turn the 60 amp breaker on.
Is there any reason why I can't take the two top consecutive single breakers out and put the 60 amp double pole breaker there and the two single breakers in the main lug only panel? It would sure make wiring much neater rather than putting more wires down lower in that mess.
Definitely no hard feelings. For me this project is kind of exciting, in a way. Just wish the weather wasn't so cold already.
Thank you, Sir, for your understanding and help.
[automerge]1569905998[/automerge]
Another question: What is the difference between the 60 amp breakers in the two links below? Why is one $9.88 and the other $66.31? That's a big difference for the same product.
Eaton Corporation BR260 Double Pole Interchangeable Circuit Breaker, 120/240V, 60-Amp - Magnetic Circuit Breakers - Amazon.com - https://www.amazon.com/Corporation-BR260-Interchangeable-Circuit-Breaker/dp/B000BO6PCC/ref=asc_df_B000BO6PCC/?tag=hyprod-20&linkCode=df0&hvadid=198075247191&hvpos=1o4&hvnetw=g&hvrand=2898305687074851425&hvpone=&hvptwo=&hvqmt=&hvdev=c&hvdvcmdl=&hvlocint=&hvlocphy=9032687&hvtargid=pla-348114793153&psc=1
and
Steve good luck and stay in touch and that link was the right breaker.Steve yes you can take out the 2 singles out and put you 60 in them slots. 75 miles is a lot plus rain and hail wow it’s 90 + degrees I NC and so humid are they a Lowe’s or Home Depot bear you. As far as the price the only thing I can think of is that make sure you get a 60 amp double pole breaker with the same name brand
Sorry about my spelling, I should proof read before sending LOLSteve yes you can take out the 2 singles out and put you 60 in them slots. 75 miles is a lot plus rain and hail wow it’s 90 + degrees I NC and so humid are they a Lowe’s or Home Depot bear you. As far as the price the only thing I can think of is that make sure you get a 60 amp double pole breaker with the same name brand
[automerge]1569932790[/automerge]
Steve good luck and stay in touch and that link was the right breaker.
Steve don’t buy the $ 66.00 breaker the difference is the rating of the breaker which won’t hurt or help you. Buy tha amazon breakerSteve yes you can take out the 2 singles out and put you 60 in them slots. 75 miles is a lot plus rain and hail wow it’s 90 + degrees I NC and so humid are they a Lowe’s or Home Depot bear you. As far as the price the only thing I can think of is that make sure you get a 60 amp double pole breaker with the same name brand
[automerge]1569932790[/automerge]
Steve good luck and stay in touch and that link was the right breaker.
[automerge]1569933443[/automerge]
Sorry about my spelling, I should proof read before sending LOL