A customer has called to say their RCD is tripping. I was planning to go tomorrow expecting a few N-E tests, identify the circuit, break it down etc.

They called again to say nothing was now working (2 separate RCD's feeding 2 separate boards) and could I come straight away. I only had an hour spare and explained this.

N-E IR test 0.7MΩ on one CU and 20MΩ on the other.

Measured voltage at the incoming supply 114V, then it went to 240V, then it went to 182V over a period of perhaps a few minutes, it continued to fluctuate.

With everything switched off the meter continued to spin, albeit incredibly slowly, almost imperceptible, but it continued to spin uniformly in the slow manner above.

Quick look outside at the overhead supply cable and I 'think' I could see scorch marks on the shroud of one of the cables where it attached to the house wall (separate line and neutral). Speaking factually I would have to just say 'dark black' areas' compared to the other shroud. DNO contacted who are there at present.

I guess my question is would this voltage fluctuation cause the RCD to trip? I believe it would from what I have read but I am not sure why as it is a residual 'current' device'?
 
Last edited:
Nothing to do with voltage.

There will be current leaking somewhere.

Not sure I agree with this. If the incoming supply is varying by a large amount then the RCD might react accordingly.

Just today I was investigating a RCD trip - with ALL the circuits completely disconnected from the CU, the RCD would not reset. Outside in the road UKPN were doing things - I did wonder if it was related!
 
.......Measured voltage at the incoming supply 114V, then it went to 240V, then it went to 182V over a period of perhaps a few minutes, it continued to fluctuate.......
I'd be far more concerned about this than the RCD tripping. If the fluctuating voltage is due to a floating neutral on the DNO supply then there's a high likelihood it could rise far above 240v as well resulting in appliance damage. Also if there's a poor neutral joint on the supply side it could possibly cause RCD nuisance tripping if there was arcing involved.
 
Very unlikely bit are the Rcd's 'Active 'as opposed to 'Reactive' which would normally be encountered.
 
Glad I got the DNO straight out! The customer has just rang me and said the DNO have just bridged the neutral as it had pretty much melted. They said the DNO had sung my praises at noticing the 'scorched shroud' so high up. I know it sounds crap singing your own praises, but I feel good!

This article (see below, point 14) mentions about dips in voltages tripping RCD's that's why I mentioned it, plus the RCD's are no longer tripping now whereas before the joint was bridged one of them tripped intermittently and the other one would not switch on at all. I simply don't know why the dip (very large dip) trips the RCD.

View attachment understanding RCD's and tripping problems..pdf

14. Mains-borne disturbances such as
spikes, voltage surges and dips, a
lightning strike and the operation of
distribution network switchgear and
protective devices combined with
capacitance to earth within the
installation can cause unwanted RCD
operation. A filter may be of
assistance.
 
Last edited:
especially on a pme system, a damaged supply neutral could result in current flowing through bonding and earthing thus causing the RCD to see an imbalance.
 
especially on a pme system, a damaged supply neutral could result in current flowing through bonding and earthing thus causing the RCD to see an imbalance.

Its a TT Tel:)
Ha! Could have just put it's TT T. Christ that's bad.​
 
Glad I got the DNO straight out! The customer has just rang me and said the DNO have just bridged the neutral as it had pretty much melted. They said the DNO had sung my praises at noticing the 'scorched shroud' so high up. I know it sounds crap singing your own praises, but I feel good!

This article (see below, point 14) mentions about dips in voltages tripping RCD's that's why I mentioned it, plus the RCD's are no longer tripping now whereas before the joint was bridged one of them tripped intermittently and the other one would not switch on at all. I simply don't know why the dip (very large dip) trips the RCD.

View attachment 32158

14. Mains-borne disturbances such as
spikes, voltage surges and dips, a
lightning strike and the operation of
distribution network switchgear and
protective devices combined with
capacitance to earth within the
installation can cause unwanted RCD
operation. A filter may be of
assistance.
Every day is a school day. Learning all the time.
 
A varying voltage or brownout in its own right will not cause a trip. However an arcing connection can produce violent transients and radio-frequency oscillations. You might see a voltage reading drifting about on your DMM in which an oscilloscope would reveal random pulses from zero to the instantaneous voltage of the supply and back again, or anywhere in between.

I=C.dV/dt, or in words the current through a capacitance is proportional to the rate of change of voltage. Capacitive leakage goes on all around us all the time in every energised circuit and appliance; 2.5 T+E leaks around 8μA per metre simply because of the stray capacitance unbalance, a typical LCD TV power supply leaks maybe 0.2mA through its interference suppressor capacitors. But these are at a sedate 50Hz; feed them some voltage transients with a wavefront 100 times steeper and those suppressors will be passing tens of mA to earth. If that goes on long enough for the RCD to respond, as it might with a heavy connection arcing away merrily, a trip is likely.
 
A varying voltage or brownout in its own right will not cause a trip. However an arcing connection can produce violent transients and radio-frequency oscillations. You might see a voltage reading drifting about on your DMM in which an oscilloscope would reveal random pulses from zero to the instantaneous voltage of the supply and back again, or anywhere in between.

I=C.dV/dt, or in words the current through a capacitance is proportional to the rate of change of voltage. Capacitive leakage goes on all around us all the time in every energised circuit and appliance; 2.5 T+E leaks around 8μA per metre simply because of the stray capacitance unbalance, a typical LCD TV power supply leaks maybe 0.2mA through its interference suppressor capacitors. But these are at a sedate 50Hz; feed them some voltage transients with a wavefront 100 times steeper and those suppressors will be passing tens of mA to earth. If that goes on long enough for the RCD to respond, as it might with a heavy connection arcing away merrily, a trip is likely.

Nicely and succinctly explained...it did cross my mind,when Happyhippy listed the changes in voltage,that these were not "true" figures,and probably the meter "averaging out".

The best way i ever saw this demonstrated,was as a kid,where my dads mate asked me "when is a known voltage,not a known voltage?"

His demonstration consisted of a piece of card,used of all things,for making wool pom-poms,which had a couple of dozen wraps of bare (non-lacquered) copper wire turned round it,at 1/16" intervals.

He lay this on the bench,and connected one end to line voltage. Then,with a Tandy multimeter,he stroked the test probe across the windings.

Anywhere he stopped,gave full voltage,going very slowly,gave peaks to full voltage,and by increasing the speed of stroke,varying "steady" voltages could be produced,which were much less than line voltage.

I suppose we could have gone fishing instead,but crude demonstrations such as i have described,allowed instant understanding,years later,of the principals involved in for instance,how speed control boards operate on proportional coils,electric over hydraulic.

Oh,and don't let your 8 year old take the above demonstration kit in,to his "show and tell"...it will distract the other kids,from their cursive,accusative,and possessives :cheesy:
 
A varying voltage or brownout in its own right will not cause a trip. However an arcing connection can produce violent transients and radio-frequency oscillations. You might see a voltage reading drifting about on your DMM in which an oscilloscope would reveal random pulses from zero to the instantaneous voltage of the supply and back again, or anywhere in between.

I=C.dV/dt, or in words the current through a capacitance is proportional to the rate of change of voltage. Capacitive leakage goes on all around us all the time in every energised circuit and appliance; 2.5 T+E leaks around 8μA per metre simply because of the stray capacitance unbalance, a typical LCD TV power supply leaks maybe 0.2mA through its interference suppressor capacitors. But these are at a sedate 50Hz; feed them some voltage transients with a wavefront 100 times steeper and those suppressors will be passing tens of mA to earth. If that goes on long enough for the RCD to respond, as it might with a heavy connection arcing away merrily, a trip is likely.

Yeah, I was thinking it was probably that too :innocent:
 
I have known loose connections upstream of an RCD to cause the RCD to trip. Sounds a bit like that but on a grander scale..
 