youngspark

Im at the fuse board and there is a fault with one of the lighting circuits. Cut a long story short when the Live is in the breaker the neutral becomes live aswell.
So I presume its a short circuit, I isolate the power and test continuity between Live a Neutral (My tester is calibrated and I tested on a known source before hand) but there is no continuity between the two!!??
Has anyone.... I mean anyone!!! Got an explanation for this?
 
What voltage is between them?, isolate every other circuit on the board and then test, Neutrals are meant to be "live" by the way
 
So, you have the line in the breaker and juiced up. Is the neutral dangling in fresh air when you measure the voltage, or in the neutral bar. Are any lights switched on?
 
The voltage is 240v between the Neutral and Earth, I isolated all of the circuits in the board and then tested it and still the same result
 
Yes the line in the breaker is livened up, the neutral is dangling in fresh air when I tested it. I don't no if the lights were on or off
 
Check all the lights are off then measure again...


edit: But Sintra has a good point!
 
sounds to me like you have lost your neutral if you have removed the neutral from the board then you will get 230volts on the neutral between the earth and neutral , not a very clever thing to do as you could electricute yourself if you touch it, to test it properly do an r1r2 test to ensure you have good continuity on the circuits then do an r2rn to ensure you have neutral continuity
 
so the N is dangling and there are 1 or more lights switched on. as the circuit is open circuit at the n END, then you will have 0 volt drop across the load, therefore you will get the line voltage on the N.
 
I was shocked as well (not literally) and that's what I thought about the polarity but it still doesn't explain why there is no continuity between the Line and Neutral conductors?
 
if all the lamps are low energy you may not get a direct continuity reading due to the electronics in the lamp, depends on the electronics of the lamp , i am asuming the light switches have been switched on
 
You're reading 240v through a lamp which, if it's say a 60W filament lamp will have a resistance approaching 1k ohm - too high for your continuity tester.
 