What is the max resistance at the time of installation permitted on customer earth rods in a TT supply?
What is the max resistance at the time of installation permitted on customer earth rods in a TT supply?
200 Ohms is what is considered to be stable, ideally you should be aiming for a reading considerably lower than that, i small nest of rods i recently fitted, I achieved 2.5 Ohms.
I guess I should drive them deep even if I get a low ohm reading with a 6 foot rod in the event the top layer of earth dries up.
I guess I should drive them deep even if I get a low ohm reading with a 6 foot rod in the event the top layer of earth dries up.
obviously you're not in the UK. it's almost permanent monsoon here. nothing can dry up. :devilish:
I thought you were NICEIC? Their version of that utter nonsense is 100ohm not 200.
Why exactly is 200 ohms max idiotic Dave ? With a decent quality 30 ma RCD you'll get perfectly reliable and acceptable [fast] disconnection times under fault conditions at much higher Ze than that. Here in Cornwall the ground is often very hard and rocky and you could easily spend a whole day trying to get multiple rods in and that would be with some luck, just not competitive I'm afraid.