200 Ohms is what is considered to be stable, ideally you should be aiming for a reading considerably lower than that, i small nest of rods i recently fitted, I achieved 2.5 Ohms.
 
What is the max resistance at the time of installation permitted on customer earth rods in a TT supply?

The regulations require that a stable and reliable value of Ra be achieved.
What is stable will depend entirely on ground conditions and soil resistivity.
Deep rods in multiple locations are the key to achieving stability.

No doubt someone will come on here to quote the idiotic 200ohm nonsense which has been misconstrued from a note in the regulations. The NICEIC have their own version of this which is 100ohm.

The problem it seems is that there are a lot of people who can't cope with the idea that a good and stable value will be very different in different parts of the country.
A value of 300ohms achieved with 4x 8' rods will be much more stable and therefore better than 50 ohms achieved with a single 4' rod
 
depends on the ground. some areas give good results with 4ft. and others struggle with 12 ft.
 
I guess I should drive them deep even if I get a low ohm reading with a 6 foot rod in the event the top layer of earth dries up.
 
I guess I should drive them deep even if I get a low ohm reading with a 6 foot rod in the event the top layer of earth dries up.

obviously you're not in the UK. it's almost permanent monsoon here. nothing can dry up. :devilish:
 
Why exactly is 200 ohms max idiotic Dave ? With a decent quality 30 ma RCD you'll get perfectly reliable and acceptable [fast] disconnection times under fault conditions at much higher Ze than that. Here in Cornwall the ground is often very hard and rocky and you could easily spend a whole day trying to get multiple rods in and that would be with some luck, just not competitive I'm afraid.
 
give it another 10 years and google will have every property in the world earthed by satellite
 
Why exactly is 200 ohms max idiotic Dave ? With a decent quality 30 ma RCD you'll get perfectly reliable and acceptable [fast] disconnection times under fault conditions at much higher Ze than that. Here in Cornwall the ground is often very hard and rocky and you could easily spend a whole day trying to get multiple rods in and that would be with some luck, just not competitive I'm afraid.

Its idiotic because the idea that you can set a blanket figure for all parts of the country with the myriad different soil conditions and ground types is ridiculous.
There are parts of the country where multiple deep rods cannot get the Ra lower than 200ohm but it will be stable, and someone would waste a lot of time and money trying to achieve the magic 200ohm when it is entirely pointless. And then there are other places where you can get <50 ohms with a single 4' rod and this will not be stable at all.

I've happily signed off an installation with an Ra around 250ohms which we had achieved with a 16' rod at each of the four corners of the house. From the initial testing before we started first fix I realised it was going to be a swine so had ducts put in to get earth wires to the locations.
 
I thought you were NICEIC? Their version of that utter nonsense is 100ohm not 200.

Very true, personally being one with little experience of TT systems I aimed on that last one to get a good reading and didn't want to settle for any less.

what I would say is that I measured the rods as I drove them in and it's very true that the deeper you go the better the result so I can only recommend going as deep as you can.

i think 3 rids deep it's quite s good depth and not too difficult to get to with a lump hammer if you don't have a better method of driving them in.

i think there's a limit to how far you go with a nest as you might keep banging rods in nice and deep and joining them together and it not making much difference so to you accept defeat at say 80 ohms or do you keep trying?

the only reason I kept going was because it seemed easy Ish to put them in and each stack gave good results.
 
Very true, personally being one with little experience of TT systems I aimed on that last one to get a good reading and didn't want to settle for any less.

what I would say is that I measured the rods as I drove them in and it's very true that the deeper you go the better the result so I can only recommend going as deep as you can.

i think 3 rids deep it's quite s good depth and not too difficult to get to with a lump hammer if you don't have a better method of driving them in.

i think there's a limit to how far you go with a nest as you might keep banging rods in nice and deep and joining them together and it not making much difference so to you accept defeat at say 80 ohms or do you keep trying?

the only reason I kept going was because it seemed easy Ish to put them in and each stack gave good results.



what do most of your DNOs require?
 
The regulations require that a stable and reliable value of Ra be achieved.
What is stable will depend entirely on ground conditions and soil resistivity.
Deep rods in multiple locations are the key to achieving stability.

No doubt someone will come on here to quote the idiotic 200ohm nonsense which has been misconstrued from a note in the regulations. The NICEIC have their own version of this which is 100ohm.

The problem it seems is that there are a lot of people who can't cope with the idea that a good and stable value will be very different in different parts of the country.
A value of 300ohms achieved with 4x 8' rods will be much more stable and therefore better than 50 ohms achieved with a single 4' rod

A misleading statement.
The regulations merely state that account is taken of the effect of soil drying and freezing, and of a possible increase in resistance due to corrosion. There is also a vague reference to values exceeding 200 ohms being unstable. That is somewhat at odds with the myriad self appointed TT regulatory authorities on this forum.
 
Ah I mistakenly thought that you meant 200 ohms was too HIGH Dave, but seems we're on the same wavelength.

Fair enough, especially at the bottom of the scale where you have the domestic installations, as you move up to bigger installations with large sites and multiple buildings then there comes a point where you really have no excuse not to get a sub-1ohm Ra.
 

Reply to TT earth electrode in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Might be a silly question, but can a tt supply come into a property via underground . This property in question, has no overhead cables...
Replies
22
Views
885
Hi all, Would like some advice on the below. Context: Rural French domestic installation TT system Earth rod is situated inside the property...
Replies
6
Views
1K
Now I understand why so many people in US have stories of computers blowing up during thunder storms. This is a pretty dumb rule for ground...
Replies
2
Views
493
Has anyone here got experience of doing a soil / earth resistance survey for the design of a large-ish site? We might be looking at a fenced area...
Replies
1
Views
422
Need some advice, I have 7 static caravans to connect which need to be connected via TT 1. All the vans have a 30ma RCD main switch internally...
Replies
6
Views
875

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock