Might be a silly question, but can a tt supply come into a property via underground .
This property in question, has no overhead cables supplying it but looks like it might have an earth electrode somewhere.
Thanks.
 
Have you any photos?

While I have never worked on them, I have seen terraced houses in London that were TT supplies fed from what looked like normal underground cables.
 
20240308_122736.jpg
 
Last edited:
The earth cable on the right of met, just dissappears into the ground with the service cable apparently.
I can't be sure, but that looks smaller than 16mm, maybe as small as 6mm? That would be consistent with it being a TT rod and not a supply TN earth.

You might find Zs is very low like TN if bonded services are large and/or linked to TN supplies in other houses, but if you can identify the conductor that is the means of earthing then a Ze test would confirm it is likely TT if somewhere in the, say 5 ohm to 200 ohm region.

Can you see if it has an incomer delay RCD, or if all boards are all RCD/RCBO?
 
I belive that it is a dual rcd plastic cu.
I think the Lh earth looks to be 16 or maybe 10 mm, if compared to the size of the incomer.
 
I can't be sure, but that looks smaller than 16mm, maybe as small as 6mm? That would be consistent with it being a TT rod and not a supply TN earth.

You might find Zs is very low like TN if bonded services are large and/or linked to TN supplies in other houses, but if you can identify the conductor that is the means of earthing then a Ze test would confirm it is likely TT if somewhere in the, say 5 ohm to 200 ohm region.

Can you see if it has an incomer delay RCD, or if all boards are all RCD/RCBO?
I can't seem to view the pic but if it is 6.0 this doesn't mean too much.
 
Can't help wondering what the separate RCCB is supplying.

Has all the hallmarks of an electric shower with no overcurrent protection, although the round cable suggests I could be wrong.
 