something inboard of the measured Ze point is causing this....

as you wouldn`t expect a value to suddenly shoot up by something in the order of 35 ohms...would you....

so i would suggest you start with the earth bar terminations....then move on from there....
 
sorry Archy...yep quite rite...

what i meant was the (R1 R2) is 35 ohms...

so for a start that aint rite...is it...

Sorry mate.. still wrong.
Ze is 175
Zs is 145

You cannot calculate R1 + R2 by taking one from the other. Zs has parallel paths, which is why it is lower
 
Glenn, he's reading 35Ohm LESS at the SO than his Ze, presumably parallel paths.


edit...great minds Andy! :-)
 
Sorry mate.. still wrong.
Ze is 175
Zs is 145

You cannot calculate R1 + R2 by taking one from the other. Zs has parallel paths, which is why it is lower
OK...
so still the value of (R1 R2) is high....
and in fact given the parrallel paths would be worse if such parrallel paths were removed...

so the point is...the value of (R1 R2) is still miles too high.....yes?

- - - Updated - - -

oh rite....
sorry..
just re read it....

- - - Updated - - -

wondered where i was going then....
 
rite...
so for a start your circuit impedence (Zs) is 35 ohms...
what do you think?..

no. his Zs is lower than Ze due to parallel paths ( water and gas bonds). obviously, on TT systems he's got to rely on the RCD/s for fault protection Zs max. 1667 fo a 30mA RCD.
 
let you off this time being as how it's friday, pi$$ing down, and before beer time.
 