so why is it not tripping at 5x now,and as i said earlier the other day it was not tripping at 1x
 
Shouldn't that be ..... Ra...aarrgghh!!!!! :devil2:

I must say , you are being very congenial today Glenn ! Are you really going for a moderation spot !?:leaving:
well...its like this...

if i have screwed up on something.....then i have to stand and take fire....

lets face it..i am usually first in the que to dole it out....
 
so why is it not tripping at 5x now,and as i said earlier the other day it was not tripping at 1x
As I said, have you ramp tested the RCD to see what it trips at? Also, is it the only RCD, are you getting correct times for any others?
 
it does mate
OK...

so i assume the instrument is working correcty...and the test leads interface with it securely...and are not damaged...

thats the place to start...check instrument first....then move on...

- - - Updated - - -

just got there first Mike...lol...
 
Callum, where are you testing the RCD at?
You should do it at the device itself with all loads/ccts disconnected.
 
The other day meter read 400ms and it never tripped,but today on 1x it tripped and 5x read 25v at a socket outlet.
 
the 25v is due to the fact no mains power is at the socket Callum, did you test the trip at times half as asked??????????????????????????
 
stop speaking sense archy, you obviously have not started drinking yet :earmuffs:

On my 2nd large bottle of Beck's actually.
Sometimes, sense just slips out by chance, can't help it!
I'm seeing the doctor about it early next week.
 