so why is it not tripping at 5x now,and as i said earlier the other day it was not tripping at 1x

I would say your meter is set at 25 volts for touch voltage limits and as your RA is high you meter is now stopping the test on 5 X due to the touch voltage exceeding 25 V. 25/0.15 = 166 Ohms etc etc
 
The other day meter read 400ms and it never tripped,but today on 1x it tripped and 5x read 25v at a socket outlet.


Did it not display >400 ms & >25 V ?


I should of read all the posts before answering as I am getting confused !!!!
 
Last edited by a moderator:
Did it not display >400 ms & >25 V ?


I should of read all the posts before answering as I am getting confused !!!!


The other day on rcd x1 it read 400ms and not tripping but at 5x tripped on the max 40ms,
today it tripped on the 1x at about 36ms but on the 5x it came up at 25v and power was on.
 
I would say your meter is set at 25 volts for touch voltage limits and as your RA is high you meter is now stopping the test on 5 X due to the touch voltage exceeding 25 V. 25/0.15 = 166 Ohms etc etc

Where is 1.5 coming from , genuine question.

I'm guessing he doesn't really understand his instrument properly
 