Back to the OP, maybe you should start again as I'm totally confused by this thread.
so why is it not tripping at 5x now,and as i said earlier the other day it was not tripping at 1x
The other day meter read 400ms and it never tripped,but today on 1x it tripped and 5x read 25v at a socket outlet.
Did it not display >400 ms & >25 V ?
I should of read all the posts before answering as I am getting confused !!!!
well...its like this...
if i have screwed up on something.....then i have to stand and take fire....
lets face it..i am usually first in the que (QUEUE) to dole it out....
Did it not display >400 ms & >25 V ?
I should of read all the posts before answering as I am getting confused !!!!
I would say your meter is set at 25 volts for touch voltage limits and as your RA is high you meter is now stopping the test on 5 X due to the touch voltage exceeding 25 V. 25/0.15 = 166 Ohms etc etc
Where is 1.5 coming from , genuine question.
I'm guessing he doesn't really understand his instrument properly