There is no requirement for a protective device on a TT system to be double pole just that it disconnects in the event of a fault.
 
My interpretation is that part of the installation is on an RCD and part isn't, it's possible that a N-E fault on the RCBO circuit could result in the other RCD operating for an unrelated fault because a parallel path would remain in place even if the RCBO tripped. A DP RCBO would prevent that. I do not think it is a requirement, but if possible I would fit a DP device if I was altering the circuit protection as part of the work carried out.
 
My interpretation is that part of the installation is on an RCD and part isn't, it's possible that a N-E fault on a single pole RCBO circuit could result in the other RCD operating for that fault because a parallel path would remain in place even if the RCBO tripped. A DP RCBO would prevent that. I do not think it is a requirement, but if possible I would fit a DP device if I was altering the circuit protection as part of the work carried out.

In my head it sounds like a tenby split load 16th ed board with first half Circuits direct from main switch and second half 30 mA rcd protected, thats the issue i usually find

It shouldnt affect the rcd downstream with an rcbo in place on the unprotected side but if there was another rcd (e.g. 100mA s type) between the origin and the new single pole rcbo, the N-E fault on the rcbo circuit would likely effect this device even when rcbo has tripped open and also cause the rcd to trip if sufficient load was applied through it

As such a double pole rcbo would be required to completely isolate said fault

Thats my understanding for what its worth

If an N-E fault would effect downstream rcd devices then i should think we would be in trouble combining RCDs onto PME supplies?
 
Last edited:

Reply to TT system, RCD or RCBO in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Im suppling distribution circuits and want to use the largest possible RCD available to avoid nuisiance tripping (its for outdoor street furniture...
Replies
2
Views
871
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
877
Hi all. Sort of an interesting one. I had a call from a client to say she is getting a shock when using the shower. I told her not to use it and...
Replies
15
Views
1K
I try to keep out of Domestic work but I have a problem at home. Currently I have a wylex fuse board with re-wire fuses. they are great because...
Replies
55
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock