Unless I've missed something this sound like classic symptoms of an N/E fault on another circuit, i.e. RCD trips when heavy load applied (from a circuit that is itself OK) and when earthing is good.
No. I've got a clamp meter I use for earth leakage and it didn't even make a reading.
If there was any earth leakage from the shower still, the RCD would definitely trip. I'm fairly certain this isn't a faulty shower or cumulative leakage either.
)No. I've got a clamp meter I use for earth leakage and it didn't even make a reading.
If there was any earth leakage from the shower still, the RCD would definitely trip. I'm fairly certain this isn't a faulty shower or cumulative leakage either.
Unless I've missed something this sound like classic symptoms of an N/E fault on another circuit, i.e. RCD trips when heavy load applied (from a circuit that is itself OK) and when earthing is good.
The clamp meter is a Dilog DL6507 It didn't even raise an eyebrow. IR test on 500v for shower when hot was >200Mohms.

Sorry - assumed wrong
Then - shower has borrowed neutral from next door lol![]()
But then why only the shower causing the problem?
Unless I've missed something this sound like classic symptoms of an N/E fault on another circuit, i.e. RCD trips when heavy load applied (from a circuit that is itself OK) and when earthing is good.
Because it's probably the heaviest load in the property, and depending on the resistance of the N/E fault compared to the supply, it takes a certain minimum load to drive 30mA through the fault. You might get the same result with 9kW of heaters plugged in but the OP probably hasn't tried that. I did ask whether the IR on the other circuits has been tested but not sure about the answer yet.
Mark It Might be worth doing IR tests on other circuits to check this , if the place is empty then the only thing pulling any real load would be the shower but thinking about it, you would of thought you would get the same fault with the bonding disconnected as you still have the CPC connected, so It could be earth leakage from next door