Lucien Nunes
Sorry, didn't connect that answer with that question. So the whole installation passes an IR test between N&E under the same conditions as the tripping occurs? If you unplugged appliances to do the test, and reconnected them afterwards, there is a small possibility that one of them contains an N/E fault.
Disconnecting the bond also points towards this explanation. With a normal case of earth leakage, whether Ze is 0.7 or 85 ohms won't make any difference, even that magic number 1667 ohms will only drop 50V of the p.d. driving the leakage. But with an N/E fault you have a low resistance path in parallel, the p.d. across the fault is tiny and increasing the Zs by a factor of 120 by disconnecting the bond would have reduced the leakage to a fraction of the current that first caused the trip. That is why I think this must be carefully ruled out, because the symptoms fit exactly
Disconnecting the bond also points towards this explanation. With a normal case of earth leakage, whether Ze is 0.7 or 85 ohms won't make any difference, even that magic number 1667 ohms will only drop 50V of the p.d. driving the leakage. But with an N/E fault you have a low resistance path in parallel, the p.d. across the fault is tiny and increasing the Zs by a factor of 120 by disconnecting the bond would have reduced the leakage to a fraction of the current that first caused the trip. That is why I think this must be carefully ruled out, because the symptoms fit exactly