There is a 45A DP switch above the worktop, it is a gas hob hence the requirement for the socket below.

There is a double oven which is housed within a larder unit, which is within 2m of the DP switch. The oven is connected by way of a cooker outlet.

The concern is the "in" and "out" at the socket, I appreciate that I may have worded the OP a little wooly but as having not seen this method previous, I sought guidance and claification.
 
Two 6.0mms into a decent socket outlet is a piece of cake. Absolutely nothing wrong with the set up uve described IMO
 
Normally states max cable size on the double socket, and I have never seen one stating 6mm !!
But with all the "fly by" start-up, don't know what your doing, so called electrical company's who don't give a Sh*t nothing surprises me.

(that's just a general view and not personally at op)
 
Two 6.0mms into a decent socket outlet is a piece of cake. Absolutely nothing wrong with the set up uve described IMO


Only in your dreams, is it a piece of cake!! Most UK wall accessories these day's only have 10mm cable terminals, so a bit of strand cutting will be necessary to get 2 X 6mm ables into them!!
 