I would C3 it, two final circuits require individual circuit protection.
I would C3 it, two final circuits require individual circuit protection.
I would C3 it, two final circuits require individual circuit protection.

There are multiple consumer units in this EICR where it has been flagged, from what i can see most seem to be part of original installation (same cable and paired dressing). Mostly on three phase boards with no spare ways.I suspect this is the case of an existing circuit and then someone lashing another to it because they cannot be be bothered to employ correct installation methods by using an additional protective device at a spare way or advising the existing board has inadequate capacity.
I suspect this is the case of an existing circuit and then someone lashing another to it because they cannot be be bothered to employ correct installation methods by using an additional protective device at a spare way or advising the existing board has inadequate capacity.
See in day in day out and I will C3 it every time.
was the boards marked up for theI should add it has detailed labelling at each consumer unit also
All points supplied by that MCB yeswas the boards marked up for the
2 circuits to the mcb.
314-01-04 off the top of my head but I suspect you know this.
reg 314.4
when an installation comprise more then one final circuit .each final circuit shall be connected to a separate way in the distribution board .