I would C3 it, two final circuits require individual circuit protection.

It's not two final circuits, it is one, the definition of a circuit in bs7671 is very clear on this.

What basis do you have for a C3? What is the improvement that can be made? Unless this Mcb is overloaded, which is a separate matter, then nothing is improved by splitting it in to two circuits
 
I suspect this is the case of an existing circuit and then someone lashing another to it because they cannot be be bothered to employ correct installation methods by using an additional protective device at a spare way or advising the existing board has inadequate capacity.
 
I suspect this is the case of an existing circuit and then someone lashing another to it because they cannot be be bothered to employ correct installation methods by using an additional protective device at a spare way or advising the existing board has inadequate capacity.
There are multiple consumer units in this EICR where it has been flagged, from what i can see most seem to be part of original installation (same cable and paired dressing). Mostly on three phase boards with no spare ways.
 
I suspect this is the case of an existing circuit and then someone lashing another to it because they cannot be be bothered to employ correct installation methods by using an additional protective device at a spare way or advising the existing board has inadequate capacity.

Based on what evidence? Whilst this is possibly what has happened, there is nothing in the regulations to prevent a circuit being extended in this way.
If a radial socket circuit has the capacity for additional sockets, then why not extend it from the DB if that's the most logical place to connect it? Surely this is better than adding an additional joint into the circuit somewhere?
 
reg 314.4
when an installation comprise more then one final circuit .each final circuit shall be connected to a separate way in the distribution board .
 