Old argument and my mind is not swayed, I agree with the Report the OP has but not the Coding.
Old argument and my mind is not swayed, I agree with the Report the OP has but not the Coding.
Yes yes yes heard all this and 314-01-04 refers to final circuit, I will not be swayed by sideway interpretations.
This is literally the extent of it, code 2 because as they put it two circuits supplied by one MCB.
I would C3 it, two final circuits require individual circuit protection.
Why aren't you soaking up the sun, and drinking those lite beers the Yanks favour, instead of wasting your time on here. Holiday of a life time you said!!
Yes yes yes heard all this and 314-01-04 refers to final circuit, I will not be swayed by sideway interpretations.
Ooher!fight ! handbags at dawn.![]()
Wrist slapped, I was quoting from the top of my head which is generally empty.You must be on a wind up quoting reg numbers from the 16th![]()
Don't recall suggesting it complied with BS7671 nor is it a personal view. I read Reg 314.4 that each final circuit should be given individual circuit protection that is it which I C3.Westward your argument has as much logic as the neutrals in switches argument. Some people just seem to stick their head in the sand and ignore facts.
You seem to admit that it complies with 7671 and yet insist on coding it!
You need to remember that coding can cost the occupier money, a lot of money. Unless you can justify a safety issue or a departure you CANT code.
Coding because of your personal views is simply unacceptable.