Sounds like there is a lot of lashing on going on.

@westward10, not arguing with your opinion on this but out of interest, someone used the principle above, say you were adding a light to an under stairs cupboard, where the consumer unit was and all cables coming out of the CU were buried and there are no spare ways. How would you do this?
 
Unless I could enable the supply by alternative means I would suggest the consumer unit has inadequate capacity for the provision of an additional circuit.
If they wanted an additional socket in the cupboard, how would you feel about taking a spur off a RFC at the consumer unit?
 
All you are doing is the following. Still one circuit as far as i'm concerned. How is this an issue?
2 radials 1 supply.jpg
 
Well, well, well. Just look at the diagram below from an IEE Wiring Matters article. The diagram is taken from the IET Electricians Guide to the Building Regulations.
I think they have 2 radials in one MCB there or I could be seeing things.
Someone better notify the IET that their diagram does not comply with their regulations... :D

Right, thats put that one to bed. Now i'm off to bed...


Cheeky IEE.jpeg
 