Replacing 15 year old FAR Italian manifolds (2 downstairs, 1 up) with new Warmup units. However, old actuators have 4 core and new only have 2 core. Can someone please explain what the additional 2 cores are used for in the old actuators and how to modify the wiring for the new, and perhaps if at all possible supply a wiring diagram for an S Plan system with 4 zone valves - 1 for manifolds downstairs, 1 for manifold upstairs, 1 for two towel rails upstairs, 1 for hot water. Many thanks for any help.
 
4 wire actuators incorporate a switch that operates when the actuator is 'on'. This switch will be connected in parallel with the ones on the other actuators, and used to turn the boiler and pump on.
A 2 wire actuator system will have a diode connected to the 'live' wire of each actuator, the second wire from each of the diodes are all connected together and connected to a relay. The contacts of this relay are then used to switch on the pump and boiler.
 
4 wire actuators incorporate a switch that operates when the actuator is 'on'. This switch will be connected in parallel with the ones on the other actuators, and used to turn the boiler and pump on.
A 2 wire actuator system will have a diode connected to the 'live' wire of each actuator, the second wire from each of the diodes are all connected together and connected to a relay. The contacts of this relay are then used to switch on the pump and boiler.
Thank you, thats very helpful.
 
You get similar with 2 port zone valves. Some have just a blue and brown wire (plus sometimes an earth) which operates the valve motor. Some also have grey and orange wires, which connect to a microswitch which operates when the valve is open.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Guernsey
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
UFH - 4 core old and 2 core new Actuators
Prefix
N/A
Forum
Central Heating Systems
Start date
Last reply date
Replies
3

Advert

Thread statistics

Created
Gsysaxman,
Last reply from
brianmoooore,
Replies
3
Views
1,659

Advert