I’ve got a central battery system at work which has slave emergency circuits.

There is a 230VAC supplyto a transformer which then has a rectifier supplying DC to the circuits. The bulkheads are custom made with inverter inside.

I can get a Zdb at the 230V supply, thus able to calculate the Zdb at the 110V load of transformer… however when using a Megger Loop Tester (LTW425) I receive the error code “Chck” which when I looked it up says it’s lost connection and retries after a couple seconds….

I can see 56V when testing, but no luck with an impedance reading. Is it because the meter can’t test DC directly?
 
I'm not an electronics engineer but from what I understand impedance and resistance essentiall are the same thing but resistance is measured on DC and impedance is measured on AC, Z is the symbol for impedance so Zdb is impedance db, for DC it would be Rdb. So it wouldn't surprise me if test meters only worked on AC circuits.

but also, is the DC side of the things even referenced to earth? I've had it on generators in the past where you cant do any tests like Ze or RCD testing until you put a link between the N-E at the generator, I'm talking about those little portable generators they have on site BTW, not big permanent ones which should already have it.
 