G

Guybrows

Hi all, I am 2nd fixing a job that someone else 1st fixed. I hav two wire coming out from under the tiles. One is a two core. One brown and one blue. The other is a bit bigger diameter cable and one core is blue and one is grey. As i did not install it i dont know which is the sensor and which is the load. I dont want to risk it as im afraid i will blow up the sensor if i get it wrong. Does anyone no a dead cert way of finding which is which. I thought about a resitance test but i dont have the instructions to check what they should be.

Many thanks for your help:eek:
 
Hi

The only way you are going to check this for sure is with a resistance meter I reckon your elements are brown and blue?? so if you have

a. 250 watt element you should measure = 212 ohms approx

b. 500 watt element = 105 ohms

c. 750 watt = 70 ohms

d. 1000 watt = 52 ohms and so on

The sensors are normally a thermistor type which have a negative temp/ heat coeficient as heat increases resistance decreases but if you dont know the type it will be difficult so best to measure the element resistance
 
The power cable should have an earth braid incorporated! If not there should be an earthed screen above the element.
 