It would, but there are limits to what can be done in many cases for the open PEN risk. For example, if you haver external metalwork that will probably be connected (say metal outdoor lights, CCTV equipment, etc) or external plumbing that is bonded, then your options are:
- Make sure all external metalwork is isolated
- TT the supply
- Put in impractically low Ra rods
- Put in an EV charger-like system to disconnect the supply live and the CPC on a fault
The first option may be the easy one if carefully considered at the installation time, but how many existing properties will not be so isolated, and how many folk will consider the PEN fault case for fitting new stuff? And what of the DNO converting from TN-S to TN-C-S later?
Going TT is an easy option and the route in Europe, but has other down sides (as often covered discussing out building supplies), as covered above the local earth rod option is probably impractical in most cases, even were it mandated from the start (which in the UK it was not).
The last option, that of the EV charger style that opens the CPC with all live conductors is probably the simplest comprehensive fix, and would also avoid the fire/damage risk of, say, 300V supply instead of 230V if you are on a light-loaded phase when the PEN opens, but a major cost to change and not a product that is currently available for the CU.
In retrospect, smart meters could have done that and
actually been useful, but that was not considered and cost saving on the design (coupled with general incompetence of the whole project management) mean it probably never will be.
This will be a debate that runs for years...