I hope that they haven't done this as it is dangerous and illegal to combine the neutral and earth in a consumers installation in the UK.
[automerge]1596117059[/automerge]


Good question, this has the potential to be a very interesting discussion.

The third core is perfectly adequate for earthing (cpc) but not for main bonding if any extraneous conductive parts are present in the outbuilding (based on the assumption that the required size of bond is 10mm)

I assume in this scenario that main bonding is not required at the shed?

Based on these assumptions that earth rod is not necessary.

What is the earth rod actually doing electrically? That depends a little on its Ra, generally its hard to get a low enough Ra that it will make a practical difference to the earthing of a PME supplied installation. You would only start to notice it affecting the Zs of the circuit, and at the origin, if the Ra was a couple of ohms or less.
If the Ra is that low then the fault current that could flow through the rod could be higher than the 4mm CPC could safely handle and it could be non-compliant.

That earth rod, in my opinion, will in itself be an extraneous part because it is introducing an earth potential into the installation. As such it would need to be connected back to the MET by 10mm copper or equivalent.
Based on that logic it is in fact making the installation worse rather than better.

As you probably know I am an advocate of earth electrodes being connected to the MET of all installations with a PME earth, I think 10mm would be the minimum acceptable conductor size for this.
I hope that they haven't done this as it is dangerous and illegal to combine the neutral and earth in a consumers installation in the UK.
[automerge]1596117059[/automerge]


Good question, this has the potential to be a very interesting discussion.

The third core is perfectly adequate for earthing (cpc) but not for main bonding if any extraneous conductive parts are present in the outbuilding (based on the assumption that the required size of bond is 10mm)

I assume in this scenario that main bonding is not required at the shed?

Based on these assumptions that earth rod is not necessary.

What is the earth rod actually doing electrically? That depends a little on its Ra, generally its hard to get a low enough Ra that it will make a practical difference to the earthing of a PME supplied installation. You would only start to notice it affecting the Zs of the circuit, and at the origin, if the Ra was a couple of ohms or less.
If the Ra is that low then the fault current that could flow through the rod could be higher than the 4mm CPC could safely handle and it could be non-compliant.

That earth rod, in my opinion, will in itself be an extraneous part because it is introducing an earth potential into the installation. As such it would need to be connected back to the MET by 10mm copper or equivalent.
Based on that logic it is in fact making the installation worse rather than better.

As you probably know I am an advocate of earth electrodes being connected to the MET of all installations with a PME earth, I think 10mm would be the minimum acceptable conductor size for this.
Are you saying you are an advocate of earth rods on PME but only with a low enough Ra?

What is the actually use of this earth rod though? An Ra even of 2 ohm is only going to give a PFC of 115A which will not blow a 100A fuse or even an 80A fuse in the cut out.
A sub 1 Ra would though.
I suppose a low enough Ra of around 2 would be sufficient to trip the MCB's in the consumer unit?
 
Are you saying you are an advocate of earth rods on PME but only with a low enough Ra?

What is the actually use of this earth rod though? An Ra even of 2 ohm is only going to give a PFC of 115A which will not blow a 100A fuse or even an 80A fuse in the cut out.
A sub 1 Ra would though.
I suppose a low enough Ra of around 2 would be sufficient to trip the MCB's in the consumer unit?
You have answered your own question really. An earth rod is only of use if it allows sufficient current to flow in order to operate the safety devices in the system it forms part of.
 
Would it not lower touch potentials as well ?
( Not ideal but better than now't )
Yes if it had a resistance value similar to the neutral its connected in parallel with. However its actual resistance value (speaking about the 4 ft galvanized rod used in most TNC-S countries) will in reality be a hundred times or more. The result? During a line to earth fault in a "healthy" TNC-S system, the rod plays a negligible role. During a broken neutral fault it actually becomes a live extraneous part that becomes a potential hazard.
 
It is only if most properties have rods to the total Ra for the section post-fault is low enough does it help to keep potentials down. Even then it would need a lot of rods.

But then again it also needs something to be monitoring this and disconnecting the segment / getting someone to fixing it as well!
 
Last edited:
...and the question is: If there is TN-C/S sistem with distrubuted PEN, or TN-S with distributed N and P conductor, why it's important do add your own earthing electrode (example 25x4), when you already have it from substation?
Why substations with such dstribution exist, why the all world doesn't use TT system.
 
...and the question is: If there is TN-C/S sistem with distrubuted PEN, or TN-S with distributed N and P conductor, why it's important do add your own earthing electrode (example 25x4), when you already have it from substation?
Ideally you don't need earth rods with TN-C-S / TN-S as the supplier provides it. In the UK it is not a requirement, but the discussion has been made to add them to deal with the case of a PEN fault.

How successful that might be is debatable, a few rods will do nothing to divert a hundred or so amps of neutral current trying to find its way home via the earth options. But a few hundred rods or some connected to buried steel building foundations would make a difference.

Why substations with such dstribution exist, why the all world doesn't use TT system.
In the days before RCDs were common / cheap you would not be able to clear most earth faults via the OCPD. So it was much safer to have a reliable low-Z earth circuit available.

VOELCB were used for TT but were rather unreliable, and they could fail to trip if you had a parallel earth path, ironically enough :(

Now that RCDs are fairly cheap there is a stronger argument for TT, but not all locations are suitable for earth rods, and you might also have difficulties in multi-occupancy buildings around responsibility or routing for an earth rod system.

Even with RCD protection, it is less reliable than a MCB/fuse (due to the extra complexity of the electronics) in terms of definitely firing on a fault. Two RCDs in series such as a 100mA delay incomer and then RCBOs get round that issue, but at added cost (though now it is not too painfully expensive to do that).

So basically in most cases a TN provided earth is safer, but the rise of PME to save copper costs has undone some of that safety. TT avoids that aspect, but pushes reliable earthing & fault disconnection on to the consumer, and they generally can't be trusted to implement / maintain it to the same degree.
 
It is only if most properties have rods to the total Ra for the section post-fault is low enough does it help to keep potentials down. Even then it would need a lot of rods.

But then again it also needs something to be monitoring this and disconnecting the segment / getting someone to fixing it as well!
It is only if most properties have rods to the total Ra for the section post-fault is low enough does it help to keep potentials down. Even then it would need a lot of rods.

But then again it also needs something to be monitoring this and disconnecting the segment / getting someone to fixing it as well!
Now that is an interesting point but again I would query whether the installing of many more rods at individual houses would have any effect on the touch voltage for those unfortunate enough to be caught on the wrong side of a broken neutral. Take an example of a housing estate with 20 houses, each having a rod with a res of 200 ohms. Neutral breaks, affecting first 10 houses. My calculations show the touch voltage at each rod still largely dependent on the individual resistance of each individual rod and unaffected by other rods. A question like that a little unfair on a Friday but am confident you are up for it?
 
OK, if there are 10 houses after the break, then that's a combined Ze of 20 ohms (OK, there'll be some resistance in the connecting cables, but smaller by an order of magnitude). That's going to take 2.5 amps while keeping touch voltage to 50V. Now, what's the actual current going to be ? Well worst case is one or two houses on same phase have electric showers going while the oven's on for the Sunday roast - in practical terms, it's going to make the earth rods "live". A more realistic suggestion is that most houses are only taking a few amps - and being on different phases the neutral currents will largely cancel.

EDIT: Apart from touch voltage, they will also reduce the P-N imbalance seen by the properties. Even a modest improvement may make the difference between headline grabbing affects or more headline grabbing effects and "a few things get damaged".

So, a question for those of you with experience in this area, what IS a realistic expectation (or typical spread of values) of earth rod impedance ? Is it 200 ohms as here, or 2 ohms mentioned a few posts back - that's a very wide spread. Or is it a case of both of those (and worse) being the sort of values to be found in the wild ?
 
Last edited:
OK, if there are 10 houses after the break, then that's a combined Ze of 20 ohms (OK, there'll be some resistance in the connecting cables, but smaller by an order of magnitude). That's going to take 2.5 amps while keeping touch voltage to 50V. Now, what's the actual current going to be ? Well worst case is one or two houses on same phase have electric showers going while the oven's on for the Sunday roast - in practical terms, it's going to make the earth rods "live". A more realistic suggestion is that most houses are only taking a few amps - and being on different phases the neutral currents will largely cancel.

So, a question for those of you with experience in this area, what IS a realistic expectation (or typical spread of values) of earth rod impedance ? Is it 200 ohms as here, or 2 ohms mentioned a few posts back - that's a very wide spread. Or is it a case of both of those (and worse) being the sort of values to be found in the wild ?
200 would be a good average
 
200 would be a good average

Average of what? What areas have you taken your values from to get this average?
[automerge]1597436381[/automerge]
OK, if there are 10 houses after the break, then that's a combined Ze of 20 ohms (OK, there'll be some resistance in the connecting cables, but smaller by an order of magnitude). That's going to take 2.5 amps while keeping touch voltage to 50V. Now, what's the actual current going to be ? Well worst case is one or two houses on same phase have electric showers going while the oven's on for the Sunday roast - in practical terms, it's going to make the earth rods "live". A more realistic suggestion is that most houses are only taking a few amps - and being on different phases the neutral currents will largely cancel.

EDIT: Apart from touch voltage, they will also reduce the P-N imbalance seen by the properties. Even a modest improvement may make the difference between headline grabbing affects or more headline grabbing effects and "a few things get damaged".

So, a question for those of you with experience in this area, what IS a realistic expectation (or typical spread of values) of earth rod impedance ? Is it 200 ohms as here, or 2 ohms mentioned a few posts back - that's a very wide spread. Or is it a case of both of those (and worse) being the sort of values to be found in the wild ?

It's not going to be as simple as that, the current flow could be all over the shop depending on the distubution of the loads. Also the balance between the phases will be having an effect on how much neutral current there actually is.

Different areas of the UK will vary greatly for their soil reisistivity and also ease of installation of earth rods.

We could probably get a massive spread of average values just from forum members experiences.

In my area I expect to see between 20 and 30 ohms from an 8' rod and I normally install at least 2 in parallel to achieve less than 20 ohms Ra.
 
Last edited:
200 would be a good average
Average of what? What areas have you taken your values from to get this average?
[automerge]1597436381[/automerge]


It's not going to be as simple as that, the current flow could be all over the shop depending on the distubution of the loads. Also the balance between the phases will be having an effect on how much neutral current there actually is.

Different areas of the UK will vary greatly for their soil reisistivity and also ease of installation of earth rods.

We could probably get a massive spread of average values just from forum members experiences.

In my area I expect to see between 20 and 30 ohms from an 8' rod and I normally install at least 2 in parallel to achieve less than 20 ohms Ra.
Use whatever values you normally get in your area. Don't forget the question which is basically trying to establish what effect on touch voltage will the sinking of rods in individual homes have. Or to put it another way if just one house had a rod and a broken neutral occurs what would be the touch voltage at his rod?
Now in another scenario imagine every house had a rod and the same broken neutral situation occurs, would the touch voltage at the rod of house number 1 be any different? I think not
 
Or to put it another way if just one house had a rod and a broken neutral occurs what would be the touch voltage at his rod?
Now in another scenario imagine every house had a rod and the same broken neutral situation occurs, would the touch voltage at the rod of house number 1 be any different? I think not

As we have already established, many times, the touch voltage depends on the Ra.

It is most likely to be different if every installation has a rod and a different number of installations are downstream of the break in the PEN.
Without any rods or bonded extraneous parts at all the touch voltage from PEN to earth changes with every individual situation, except for a single installation, whne a break in the PEN occurs.
 
10 houses, assuming spread over 3 phases, one might assume an average neutral imbalance of around 20-40A (i.e. 1-2 houses' worth of diversity assumption). To keep touch below 50V would mean something like 1.2 ohm from 10 houses' rod-sets, so around 12 ohms per rod-set.

In some areas that is feasible, other impractical.

But really we should not have to deal with the open PEN risk as there ought to be some more central arrangement to monitor connectivity and disconnect all phases at the substation, etc.
 
ut really we should not have to deal with the open PEN risk as there ought to be some more central arrangement to monitor connectivity and disconnect all phases at the substation, etc.

Why shouldn't we have to deal with it? We put protective measures in place to minimise risks when faults occur, so why not for this type of fault?
 
Why shouldn't we have to deal with it? We put protective measures in place to minimise risks when faults occur, so why not for this type of fault?
Just it would be far more cost-effective for the DNO to take additional steps, than for the UK's electricians to deal with it in many new and existing properties.
 
Just it would be far more cost-effective for the DNO to take additional steps, than for the UK's electricians to deal with it in many new and existing properties.

And it would be safer if both the network and the installation contains provisions for protection against these faults.

Even if the DNO put measures in place to reduce the danger from these faults it won't change my opinion that installations should be taking steps to do the same.
 
It would, but there are limits to what can be done in many cases for the open PEN risk. For example, if you haver external metalwork that will probably be connected (say metal outdoor lights, CCTV equipment, etc) or external plumbing that is bonded, then your options are:
  • Make sure all external metalwork is isolated
  • TT the supply
  • Put in impractically low Ra rods
  • Put in an EV charger-like system to disconnect the supply live and the CPC on a fault
The first option may be the easy one if carefully considered at the installation time, but how many existing properties will not be so isolated, and how many folk will consider the PEN fault case for fitting new stuff? And what of the DNO converting from TN-S to TN-C-S later?

Going TT is an easy option and the route in Europe, but has other down sides (as often covered discussing out building supplies), as covered above the local earth rod option is probably impractical in most cases, even were it mandated from the start (which in the UK it was not).

The last option, that of the EV charger style that opens the CPC with all live conductors is probably the simplest comprehensive fix, and would also avoid the fire/damage risk of, say, 300V supply instead of 230V if you are on a light-loaded phase when the PEN opens, but a major cost to change and not a product that is currently available for the CU.

In retrospect, smart meters could have done that and actually been useful, but that was not considered and cost saving on the design (coupled with general incompetence of the whole project management) mean it probably never will be.

This will be a debate that runs for years...
 
It would, but there are limits to what can be done in many cases for the open PEN risk. For example, if you haver external metalwork that will probably be connected (say metal outdoor lights, CCTV equipment, etc) or external plumbing that is bonded, then your options are:
  • Make sure all external metalwork is isolated
  • TT the supply
  • Put in impractically low Ra rods
  • Put in an EV charger-like system to disconnect the supply live and the CPC on a fault
The first option may be the easy one if carefully considered at the installation time, but how many existing properties will not be so isolated, and how many folk will consider the PEN fault case for fitting new stuff? And what of the DNO converting from TN-S to TN-C-S later?

Going TT is an easy option and the route in Europe, but has other down sides (as often covered discussing out building supplies), as covered above the local earth rod option is probably impractical in most cases, even were it mandated from the start (which in the UK it was not).

The last option, that of the EV charger style that opens the CPC with all live conductors is probably the simplest comprehensive fix, and would also avoid the fire/damage risk of, say, 300V supply instead of 230V if you are on a light-loaded phase when the PEN opens, but a major cost to change and not a product that is currently available for the CU.

In retrospect, smart meters could have done that and actually been useful, but that was not considered and cost saving on the design (coupled with general incompetence of the whole project management) mean it probably never will be.

This will be a debate that runs for years...
Excellent analysis. Think you have pretty much summed up the whole issue we are facing with TNC-S as well as supplying the potential solutions. Undoubtedly not incorporating a mechanism to uncouple the DNO, s supply from the consumers installation under broken neutral conditions is an opportunity missed
[automerge]1597516435[/automerge]
As we have already established, many times, the touch voltage depends on the Ra.

It is most likely to be different if every installation has a rod and a different number of installations are downstream of the break in the PEN.
Without any rods or bonded extraneous parts at all the touch voltage from PEN to earth changes with every individual situation, except for a single installation, whne a break in the PEN occurs.
Want to come back to you on this one. Am still of the view that the rods down stream of the break won't matter a jot but need to fully tease it out.
 

Reply to Understanding the relationship between TNCS, TNS and TT in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
446
Hi Guys, Long time member and not a regular user here. I do pop in here when the odd unknown pop's up and unable to locate an electrical dilemma...
Replies
4
Views
853
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
425

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock