Dartlec
Arms
Are the bathroom lights downlights? Unless there is a low ceiling they may well be above the 2.25m zone requirement anyway, which should not attract a C2.
As you say, the C2 listed on Page 2 should be noted on page 6 under 6.6, where it is ticked, so the document is inconsistent at best.
If the bathroom light is within the zones and isn't appropriately IP rated (it's not always obvious) then perhaps changing it will be sensible in any case as any report would pick that up as a C2 and it is at least a potential issue of safety.
As pointed out, as long as you have documented proof of the light being changed then you have complied with your requirements so it is not necessary to obtain another report just to show satisfactory.
If the install is a flat and/or relatively new, then the LIMs on the items 1.x are not necessarily a concern - Is the meter perhaps in a remote room elsewhere in the complex? In which case the property management company may have some responsibility for the feed to each flat and you may be able to ask them for something in writing that their part of the installation is safe..
In theory, all LIMs on a report are agreed with the client though, as you are the one ordering the work and with the responsibility to ensure safety - so if it's an older installation or those parts are easily accessible its more of a concern that they weren't even visually checked.
As you say, the C2 listed on Page 2 should be noted on page 6 under 6.6, where it is ticked, so the document is inconsistent at best.
If the bathroom light is within the zones and isn't appropriately IP rated (it's not always obvious) then perhaps changing it will be sensible in any case as any report would pick that up as a C2 and it is at least a potential issue of safety.
As pointed out, as long as you have documented proof of the light being changed then you have complied with your requirements so it is not necessary to obtain another report just to show satisfactory.
If the install is a flat and/or relatively new, then the LIMs on the items 1.x are not necessarily a concern - Is the meter perhaps in a remote room elsewhere in the complex? In which case the property management company may have some responsibility for the feed to each flat and you may be able to ask them for something in writing that their part of the installation is safe..
In theory, all LIMs on a report are agreed with the client though, as you are the one ordering the work and with the responsibility to ensure safety - so if it's an older installation or those parts are easily accessible its more of a concern that they weren't even visually checked.