Hi all you guys/gals out there was wondering if anyone could offer advice on the following:
I was recently asked to fill in an upgrade of supply form for a customer. A fabrication company. I went out to the premises and took some readings of their consumption. They have a 100 amp 3 phase supply at the moment with the standard cut out and meter set up they are using L1=42.5amp L2=90amp L3=92amp. They need to fit some new additional equipment. Am i right in thinking to go above this size of supply would involve fitting an ISU and CT metering ? also i was asked on the form about information for welding equipment which they have 7 of it asked for Pulses per minute any advice would be appreiciated.
Regards Richard
I was recently asked to fill in an upgrade of supply form for a customer. A fabrication company. I went out to the premises and took some readings of their consumption. They have a 100 amp 3 phase supply at the moment with the standard cut out and meter set up they are using L1=42.5amp L2=90amp L3=92amp. They need to fit some new additional equipment. Am i right in thinking to go above this size of supply would involve fitting an ISU and CT metering ? also i was asked on the form about information for welding equipment which they have 7 of it asked for Pulses per minute any advice would be appreiciated.
Regards Richard
Be prepared for a highly variable price depending on location of sub stations, local distribution cable sizes and existing loads and the amount of road permits the supply authority may need to complete the works. They may come back and say it is not possible at the present moment to upgrade the supply, in twenty years this has happened to me twice (Both in rural locations) 