asked him to note what had tripped and gave him the option for me to call back. asked for a window within a week. he would not give me one. what it boils down to is that he is fixated on a rewire and thinks i've given him bad advice. he's had a 2nd sparks in who's told him he needs a rewire, as well as ( reported by customer) " there's not enough power coming into the house".
my advice was based on
1.visual inspection of cables at CU and accessories, no damage or insulation deterioration observed.
2. IR tests showed well over that required by BS7671.
3. all circuits had cpcs and Zs readings were within parameters.
4. above was determined after dodgy garage wiring was dissed, and a fault on the socket circuit repaired.
my advice was based on
1.visual inspection of cables at CU and accessories, no damage or insulation deterioration observed.
2. IR tests showed well over that required by BS7671.
3. all circuits had cpcs and Zs readings were within parameters.
4. above was determined after dodgy garage wiring was dissed, and a fault on the socket circuit repaired.