There are water pipes, copper and heating pipes in the area where the board will be which are all copper. However, the water supply is bonded so would imagine it will be ok and not require further bonding.
its a bit of a pigs ear at the moment how it's fed as it's got Henley blocks off the head and the 25mm SWA is joined into a bit of 16mm twin and earth, so the actual CSA at present is at the weakest point which is 6mm on the twin and earth. So this needs doing properly through a switched fuse etc, no big issue.
i am more than capable of terminating the SWA properly, I don't mind using as such but prefer to use another core or separate earth.
My only query I suppose was what the equivalent CSA or the 25mm 2 core SWA equates to, Ive got a link somewhere, let me check.
It's a pub installation, what do you expect it to be like???
It's going to be a slap dash mess that's been thrown in over the years and covered in stinking sticky yellow crap from the years of smoking in there.
Can you give a good reason why you prefer to not rely on the CPC designed in to the cable and instead add extra conductors. Especially considering that there is a strong theory that the majority of fault current will flow through the armour regardless of there being another conductor.
Do you also pull a g/y in to conduit or use 3 core MI for single phase?