I've been asked to complete some wiring on a couple units/ flats. There is one boiler and pump, to heat 2 separate heating systems. So the there's 2 programmers etc. What's the best way to go about this?
If the programmers are fed from the same supply and isolator, then no need for relays. If each prog is fed from different circuit then the valve SL outputs for each circuit will have to energise a relay, the N/O contacts of the two relays then energise the boiler SL.