Could anyone advise? I'm on the job.

New boiler and cylinder installed by plumber It's S Plan - two honeywell valves for CH and HW, wireless room stat.

I'm quite confident that the wiring centre wiring is all ok. But, the boiler is not firing up. The pump starts but no ignition.

I'm wondering if I've got it wrong at the boiler PCB.

I've got the oranges from the valves going to the 230V RT next to the main LNE power in terminal block. The 24V RT link is in.

240V is at LNE and also between N and RT 230V. That's all the cores I have going in .

Thanks
 
Have you got 230V at RT? Try removing the grey wire and link the RT terminals together.

Has the boiler got gas? Is the system up to pressure? Is the boiler going through a venting cycle?
 
You need to turn it on in the settings of the boiler.

Also you need to remove the link in the 24v stat (the white one beside Burner, marked 24V RT.
Could also do with sleeving your cables brown and blue where appropriate.
 
  • Like
Reactions: Leesparkykent
Thanks so much for your help .I really appreciate it.

I called the plumber back and he finally remembered that he hadn't turned on the gas ..... Bejeezuz ....

Thanks for comments on the sleeving and 24V link. All done.
Thanks again
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Vaillant Ecotec 630 plus Wiring
Prefix
Forum
Central Heating Systems
Start date
Last reply date
Replies
4

Thread Tags

Tags Tags
wiring

Advert

Thread statistics

Created
acvc,
Last reply from
acvc,
Replies
4
Views
6,073

Advert