Do check your settings on the meter and the battery level just in case.
Then try testing in your house as close to the origin as possible, without any switches, just the supply and see what reading you get, if it is still +40ohms then sounds like a leads or meter problem.
What reading do you get on testing resistance on the leads?
I have spent the last 2 days going through the entire house checking and testing and putting right some very sorry wiring expecially on the R2 side of things. I am happy with all of the wiring and the results that I have had on the continuity and resistance side of things. it is this very high Zs I can't seem to fathom out. The RCD is a Hager.
I have just tested at the terminals of the same socket with my 3 test leads and am now getting 0.01 ohms and 23.00 Ka.
Change your plug tester unit!
But try a few contiuity tests through the unit first and see that there is not dirt in the connections or bent pins from dragging around in your tool bag.
Edit
No hang on 0.01ohms sounds a bit low for a standard value, could be, but 23kA is too high for a domestic CU.
Gentlemen, thankyou for your time and patience. I will try again with just my probes and see what I get. Just one other question; why does a main switch RCD trip whwn carrying out Zs testing? i had one the other day, another empty house and need to go back to sort it.
Kind regards.
Post #10... :lol:
Have you got a 'no trip' setting on your MFT?
When testing Zs a current of about 20A is used to test the resistance, this will trip an RCD (and possibly a 6A MCB), no trip or trip lock limits the current to 15mA or so but may give a different reading.
I don't think some of my posts are being sent. I have tried my three probes at my socket terminals and am getting 0.01ohms with a PEFC of 24Ka. So I think the problem is solved.
Just one more thing; I had a RCD main swith ch trip on me whilst carrying out Zs test the other day. I need to go back and sort it ( It's an empty house) What could be causing the RCD main switch to trip? I was using my plug adapter again>
Many thanks.
I would still be worrying with those results.
0.01ohms for ZS??
24Ka ???
Wouldn't like to be in that house when that kind of fault current flows.
Your meter sounds f***ed - did they cock up the calibration?
something is definitely wrong here. to get a Zs of 0.01, you would have to have a -ve value for R1+R2 .l try and borrow another MFT.
Reply to Very high Zs reading in the UK Electrical Forum area at ElectriciansForums.net
Hi, I did my first EICR on a TT system today and the Zs was a lot higher than Ze+R1+R2 on everything. Zs was around 3.5 ohms on all of the ring...
OLDBOY
O
What would be the fault with a very high Zs at all sockets on a ring main, the sockets are an average of 68.10 . The lights are.67 and the is...
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...